Each baseboard heater will draw a little over 4 amps at 120 volts or 2 Amps at 240 volts. The total number of baseboards on a circuit will draw the sum of these amps. Keep the load under 80% of the amperage rating of the breaker.

User Avatar

Wiki User

14y ago
This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: What size breakers are needed for two 500 watt baseboards?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

What size cable required for3 phase 128 watt?

To answer this question a voltage is needed.


What size of solar panels is needed to charge a 12v 150ah battery with hours sunlight 10?

200 Watt Panel


If you have 1200 watt generator how much will voltage drop with 100ft extension cord?

To answer this question more information is needed. The wire size of the extention cord is needed.


What size breaker is needed for a 1100 watt microwave?

A minimum of 15-amp breaker is "needed", but a 20-amp is often required by electrical code for that situation.


What wire size needed for 120 volt 3000 watt load?

AWG # 10 wire on 30 amp circuit.


What size breaker is needed to connect 5500 watt gas powered generator?

A 5500 watt gas powered generator typically requires a 30 amp breaker for a 240 volt connection. It is recommended to consult the manufacturer's specifications to ensure the correct breaker size for your specific generator model.


What is the formula of 2 phase power?

The formula which are needed for making of a single phase transformeri.e o/p voltage,watt,current,turn,core size,coil number,bobin size etc


How many 75 watt fluorescent bulbs are needed to give as much light as a 75 watt incandescent bulb?

A 15-watt fluorescent should produce about as much light as a 75-watt incandescent.


What size breaker should you use if you have a 1500 and a 1000 watt heater run together?

The size of the breakers depends on the voltage. According to the NFPA electrical standard (USA), if the two heaters you describe are "120 volt plug-in" then they are not allowed on the same circuit. Two circuits are needed. The largest general use circuit allowed for 120 volt receptacles is 20 amps and this will not handle your two appliances. An exception may exist if they are hard wired to a dedicated circuit, or if they are 240 volt.


What amp fuse do you use for a 100 watt bulb?

Fuses or breakers are used to protect the conductor to the load. A #14 wire conductor is rated for 15 amps. Most home circuitry is done with #14 wire. The minimum size breaker in an electrical panel is 15 amp so it looks like a 15 amp fuse or breaker can be used for a 100 watt light bulb.


What size cable to use on a 50 watt lamp?

16 AWG is plenty large enough for a 50 or 100 watt lamp.


What size wire should be used from main panel to 50 watt subpanel?

#6 wire is needed. If placing the subpanel in a garage at a good distance, it is recommended to also install a seperate ground rod .