Up to 12 on a 20 amp circuit. Up to 9 on a 15 amp circuit. But use common sense. If the circuit will be heavily loaded, as in a home office, then do not install that many.
Chat with our AI personalities
There is no limit as to the amount of circuits you can have in a garage. If you mean how many devices on a 15 amp single circuit breaker then the answer is 12. Be sure to total in light fixture outlets and switch boxes.
Assuming this is not an office of a place where lots of the outlets will be used to power items that draw lots of current on a 15 amp circuit wired with 14/2 wire I would limit it to no more than 10 outlets and lights combined. On a 20 amp circuit wired with 12/2 wire I would limit it to a 14 outlets and lights combined. There is no limit in the code. You just use common sense based on what is going to be used on this circuit.
No, but the code as of today (2012) does require tamper proof outlets.
If they're not CO/ALR outlets, there is.
ten lights per curcuitCircuit loadingIn Canada there shall be not more that 12 outlets on any 2 wire branch circuit. Such outlets shall be considered to be rated at not more that 1 amp per outlet. Where the connected load is known, the number of outlets may exceed 12 providing the load current does not exceed 80 % of the rating of the over current device protecting the circuit.