No, it is not safe to use a #8 conductor on a 50 amp breaker. A #8 conductor is only rated at 45 amps capacity. By connecting it to a 50 amp breaker, which would trip at 50 amps on an overload, would overload the conductor by an extra 5 amps. This would be a conflict against the electrical code.
No, 10 gauge wire requires the use of a 30 amp breaker. A 20 amp breaker is only used on 12 gauge wire.
Use a 30 amp breaker.
The size breaker you use is determined by the size wire used in the circuit. If you use AWG #12/2 wire then use a 20 amp breaker. If you use AWG # 14/2 then use a 15 amp breaker.
No. A 20 amp breaker needs 12 gauge wire.
25 amp breaker
No, 10 gauge wire requires the use of a 30 amp breaker. A 20 amp breaker is only used on 12 gauge wire.
No, it is not safe to use 10 gauge wire with a 30 amp breaker as the wire is not rated for that high of a current. It is important to use the correct wire gauge that matches the breaker amperage to prevent overheating and potential fire hazards. For a 30 amp breaker, you should use at least 10 gauge wire.
Use a 30 amp breaker.
Depends on the wire size used in the circuit. If you use AWG # 14 wire you must use a 15 amp breaker. If it is wired with AWG # 12 wire then you use a 20 amp breaker. If a AWG # 10 wire is used then a 30 amp breaker is required. The breaker protects the wiring from overheating so you must use the proper size breaker for the wire used.
The size breaker you use is determined by the size wire used in the circuit. If you use AWG #12/2 wire then use a 20 amp breaker. If you use AWG # 14/2 then use a 15 amp breaker.
No, it is not safe to use a 15 amp outlet on a 20 amp breaker as it can lead to overheating and potential fire hazards. It is important to match the outlet's amp rating with the breaker's amp rating for safety.
No, it is not safe to use a 20 amp outlet on a 15 amp breaker as it can overload the circuit and pose a fire hazard. It is important to match the outlet with the appropriate breaker amperage for safety.
No. A 20 amp breaker needs 12 gauge wire.
25 amp breaker
For typical residential house wiring 12 AWG wire is required for a 20 Amp breaker. If you change out the breaker for a 25 A breaker you would have to rewire the circuit with 10 AWG. In that case you could up the breaker to 30 Amps. All outlets and switches should be rated at the same voltage and current as the breaker.
The breaker you use is determined by the size of the wire in the wall not by what is being connected to that circuit. If you have 14/2 wire then use a 15 amp breaker. If you have 12/2 wire then use a 20 amp breaker. The breaker protects the wiring not the item connected.
Depends on the wire size you are using. If the generator breaker is a 30 amp then install a 30 amp breaker.