If the run is less than 100' use 4 AWG copper.

User Avatar

Wiki User

12y ago
This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: What size wire to run air handler which requires a 100 amp breaker?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

Should 25 amps breaker be replaced by 20 amps?

For typical residential house wiring 12 AWG wire is required for a 20 Amp breaker. If you change out the breaker for a 25 A breaker you would have to rewire the circuit with 10 AWG. In that case you could up the breaker to 30 Amps. All outlets and switches should be rated at the same voltage and current as the breaker.


Is the wire running to a 20amp breaker different from a wire running to a15amp breaker?

Yes, a 20 amp breaker requires AWG # 12 copper wire. A 15 amp breaker requires AWG # 14 copper wire.


Can I you use existing 8 3 wire hooked to a 30amp breaker was hooked to old electric heater to wire a heater that requires 10 2 wire its a 5000watt 240volt heater?

No, you cannot use an existing 8 3 wire hooked to a 30amp breaker for a heater that requires 10 2 wire. The wire gauge and breaker size need to match the specific requirements of the new heater to ensure safety and proper function. You will need to upgrade the wiring to accommodate the 10 2 wire needed for the 5000-watt 240-volt heater.


Can you have a 120v circuit on a 30 amp breaker?

No, electrical code typically requires that circuits be protected by a breaker that matches the wire size. A 30 amp breaker is typically used for circuits with larger wire sizes. For a 120V circuit, a 20 amp breaker is more suitable with appropriate wire size.


When installing a circuit breaker do you size the breaker to correct wire size or the device its controlling?

When installing a circuit breaker, you size the breaker based on the wire size. The breaker should be matched to the ampacity of the wire to ensure proper protection against overloads and short circuits. The device being controlled by the breaker is not a determining factor in sizing the breaker.


What size breaker does it take to run a outdoor well?

Normally AWG #10 wire on a 30 amp breaker but it really depends on the size of the pump. The pump manufacture will specify the size wire and size breaker needed.


What size wire do you need to wire a 200 am breaker box?

6


Can you use 40 amp breaker for your lights and plug ins?

If you are referring to house wiring then the answer is no. A breaker protects the wire size that is connected to the breaker. In home wiring most homes are wired with a #14 wire which is rated at 15 amps. That is why the wire is protected by a 15 amp breaker. The correct wire size to connect to a 40 amp breaker is a #8. This size wire is too large to connect to receptacles an light fixture terminals.


How big of breaker do you use for 115 volt?

Depends on the wire size used in the circuit. If you use AWG # 14 wire you must use a 15 amp breaker. If it is wired with AWG # 12 wire then you use a 20 amp breaker. If a AWG # 10 wire is used then a 30 amp breaker is required. The breaker protects the wiring from overheating so you must use the proper size breaker for the wire used.


What size breaker should you use for a tnia-10 wire?

25 amp breaker


What size wire would you use on a 30amp breaker?

AWG # 10 wire.


14 gauge wire can be on what size circuit breaker?

A 14 gauge wire is typically used on a 15 amp circuit breaker. It is not recommended to use a larger circuit breaker with a smaller wire size as this can create a fire hazard.