The formula to use is I = W/E, assuming that the single breaker is delivering 120 volts, the amperage to the circuit is 16.6 amps. A continuous load on a 20 amp breaker has to be reduced to 80% according to the electrical code. 20 x .8 = 16. So to answer the question, yes, a 20 amp breaker will support a 2000 watt load at 120 volts.
14 gauge will handle it with a 15 amp breaker. If you use 12 gauge use a 20 amp breaker.
The maximum wattage that a 30 amp breaker can handle is 30 x 230 = 6900 watts. Other variables come into play and this number will decrease depending on the load, duty time, and difference in voltage fluctuation.
Yes, in home wiring as long as it is protected by a 15 amp breaker. Remember this circuit will only handle 1800 watts and cannot be loaded to any more than 1440 watts. So if each light is 75 watts then the maximum you can install is 19.
If you use a 20 amp breaker, you would need to use 12 AWG wire. If you use a 15 amp breaker, you could use 14 AWG. As always, make certain that you comply with all local wiring codes.
The breaker protects the wiring not the boiler. 12,000 watts at 240 volts will require 50 amps. So, you will need a 60 amp breaker using AWG# 6 wire on a dedicated circuit.
Should be fine if that is all that is on the breaker.
Yes, it can.
14 gauge will handle it with a 15 amp breaker. If you use 12 gauge use a 20 amp breaker.
A 20 amp breaker can handle up to 2400 watts per hour (20 amps x 120 volts = 2400 watts).
The equation that you are looking for is I = W/E. Amps = Watts / Volts.
To calculate the amperage needed for 1500 watts at 120 volts, use the formula: Amps = Watts / Volts. In this case, it would be 1500 watts / 120 volts = 12.5 amps. Therefore, you would need a 15 amp breaker for this circuit to accommodate the power load safely.
To answer this question a voltage must be given. Watts = Amps x Volts. <<>> Answer At 115 volts ac, 30 amps equals 3,450 watts.
A 60 amp 2-pole breaker can handle up to 14,400 watts (60 amps x 240 volts). This is because a 2-pole breaker provides 240 volts, which is the typical voltage for larger appliances and machinery.
At 120 volts a 15 amp breaker can be loaded to 1800 watts before it will trip. If it is a continuous load then the electrical code states that it is only allowed to be loaded to 80%. This will be 1800 x .8 = 1440 watts. If the voltage is not 120 volts use the following equation Watts = Amps x Volts. Amps being the breaker size that is to be used.
On a 20 amp breaker, you can safely operate devices that consume up to 2400 watts (20 amps x 120 volts = 2400 watts). Exceeding this limit can trip the breaker to prevent overheating and fire hazards.
A 20 amp circuit breaker at 208 volts can handle up to 4160 watts (20 amps x 208 volts = 4160 watts). This is calculated by multiplying the amperage by the voltage to determine the maximum wattage capacity of the circuit.
For safety reasons ( and the National Electric Code) never put more than 75% load on a breaker, so for you case, 20 amp breaker x 75% = 15 amps 15 amps x 240 volts = 3600 watts 3600 watts