Best Answer

If the generator is 3-phase 120/208 v. it produces 104.21amps per phase using the formula 30,000 / (1.73 x 208 x .80). If it is 277/480 v. It gives 45.18 amps. A singlephase generator will give 125 amps at 240 volts and 62.5 amps at 480v.

User Avatar

Wiki User

โˆ™ 14y ago
This answer is:
User Avatar
More answers
User Avatar

Wiki User

โˆ™ 9y ago

A 415 v three phase system has a line-to neutral voltage of 240 v on each of the three phase wires. Each wire supplies 250,000/3 or 83,333 VA so the current is 83,333 / 240 or 347 amps.

The current in each live wire is 347 amps. If a balanced load was delta-connected to it, the load current would be 200 amps at 415 volts.

Another Answer I suspect that you are really asking what the line current, rather than the phase current, would be.... however,

Assuming the machine is supplying a balanced load, to find out the line current (and, therefore, the phase current, in the case of a star-connected machine), you simply divide the kVA by (1.732 x line voltage):

current = (250 000) / (1.732 x 415) = 347 A.

This equation applies to both star and delta connections, so If the machine was delta connected, it would supply exactly the same line current, but the load current would be the line current divided by 1.732, or 200 A.

This answer is:
User Avatar

User Avatar

Wiki User

โˆ™ 13y ago

Use the formula, amperage when kva is shown; I = kva x 1000 / 1.73 x volts.

This answer is:
User Avatar

User Avatar

Wiki User

โˆ™ 14y ago

Here, power p=2000kva

v=550 v

Now P= 1.73*V*I*COS(PHY)

ASSUMING POWER FACTOR IS UNITY HENCE COS=1

HENCE I=(2000*1000)/(1.73*550*1)

=2101AMP

This answer is:
User Avatar

User Avatar

Wiki User

โˆ™ 12y ago

Amps/3*0.8=(kva*1000)/(1.73*volts)

220v 380v

250kva 175amp 101amp

This answer is:
User Avatar

User Avatar

Wiki User

โˆ™ 9y ago

For a 415 v three-phase generator the current is 278 amps for 200 kVA.

This answer is:
User Avatar

User Avatar

Wiki User

โˆ™ 9y ago

To answer this question correctly, the voltage of the generator must be given.

This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: How many amps for 250 kva generator per phase at 415v?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

How many amps will a 240 volt single phase 15 kva generator supply?

62.5 amps


How many amps for 1010 KVA generator per phase?

To answer this question the voltage of the generator must be given.


How many amps does a 18000 watt generator supply at 240 volts?

A 18000 watt generator supplying power at 240 volts would supply 75 amps (18000 watts รท 240 volts = 75 amps).


How many output amps is a 75 KVA generator single phase?

The formula you are looking for is , A = kva x 1000/Volts.


How many amps will a 240 volt single phase 20KW generator supply?

Typically 75 amps on natural gas, 85 amps using propane. Peak amps(for less than a second) to start a big appliance, like an A/C condenser, are 130.


How many output amps is a 75 KVA generator?

It depends upon the Generator system voltage. For 3 Phase, 600 Volt system, it will be 73 Amps For 3 Phase, 480 Volt system, it will be 90 Amps For 3 Phase, 208 Volt system, it will be 208 Amps


How many amperes for 3 phase 220v 5 tonner?

50 Amps Single Phase 20 Amps Three Phase


How many amps is 5.5KVA generator good for?

5.5kva


How many output amps is a 600kva generator at 240v?

To calculate the output amps of a 600kVA generator at 240V, you would use the formula Amps = kVA / Volts. In this case, it would be 600kVA / 240V = 2500 amps.


How many watt generator to run a 150 amp service?

You will need a 50 kW generator for a single phase 120/240 volt service.


How many amps is 8500 watts generator?

To find the amperage of a generator, you can use the formula: Amps = Watts / Volts. Assuming a standard voltage of 120V for household generators, you can calculate the amperage as: 8500 Watts / 120 Volts = 70.83 Amps.


How many amps 50 hp 240 3 phase?

106 amps