Please be more specific....simply replacing the breaker with a 20 amp may cause a fire; if the cable is sized for 15 amp and is overloaded. Your 15 amp breaker is probably feeding #14 wire. The use of a 20 amp breaker requires at least a #12 wire be used. Fire hazard if breakers and wiring are not sized correctly.

User Avatar

Wiki User

βˆ™ 19y ago
This answer is:
User Avatar
More answers
User Avatar

AnswerBot

βˆ™ 5mo ago

It is not recommended to replace a 15 amp breaker with a 20 amp breaker without ensuring that the wiring and appliances on that circuit can handle the higher amperage. Using a 20 amp breaker on a circuit designed for 15 amps can create a fire hazard due to potential overheating. It is best to consult with a licensed electrician before making any changes to your electrical system.

This answer is:
User Avatar

User Avatar

Wiki User

βˆ™ 16y ago

in most circumstances #12 AWG wire is suitable for 20 amps Changing a 15 amp breaker to a 20 amp breaker even if the wiring is #12 can create a violation and or a danger depending on the circumstances of the circuit and loads involved. This topic is discussed at length in the National Electrical Code

This answer is:
User Avatar

User Avatar

Wiki User

βˆ™ 13y ago

Breaker size is dependent on the wire size used for the electrical circuit, for example a 15 amp breaker would protect a 14awg circuit and trip when a load of approximately 1800 watts is exceeded. A 20 amp breaker would protect a 12awg circuit and trip when the load exceeds approximately 2400 watts. These examples assume a voltage of 120vac.

This answer is:
User Avatar

User Avatar

Wiki User

βˆ™ 13y ago

No!

A circuit that has been designed to handle 15 amps will be pushed beyond it's limits if you install a 20 amp breaker. The risk of fire is far too great.

I agree with the above but if you find the circuit was wired with 12 gauge wire it will work just fine. It is probably wired with 14 gauge wire, however, which is too small for 20 amps.

This answer is:
User Avatar

User Avatar

Wiki User

βˆ™ 15y ago

Physically you could, but I would not recommend it. A Breaker is designed to sense current flow. If it senses too much flow, or more than it is designed to handle, then it will "break" the circuit and prevent anymore current to flow. But a breaker goes hand in hand with the current carrying capability of the wire connected to it. Wiring is designed by "gauge", or how much current it can safely carry before the heat generated by current flow, causes the insulation to melt and potentially cause a fire.

The smaller the number, the bigger the copper wire, the more current it can safely carry. For example: 6ga wire is far larger than 14ga wiring used in most homes.

So if you have a 15amp breaker, it must be connected to wiring that has a 15 amp current carrying capability. That way, in the event of runaway current (short circuit), the breaker will open, before the insulation on the wire began to break down.

If you replace a 15 amp breaker with a 20 amp breaker, you could now have a situation where your wiring is good to lets say 17 amps of current max. So if an "overload" occurred, and let's say it was at 19 amps, your wire's insulation would begin to overheat and or melt away, exposing the live copper. Meanwhile, your breaker won't see a problem, because it's not designed to sense a problem unless you exceed 20 amps. So in normal circumstances, it would be a very bad idea.

This answer is:
User Avatar

User Avatar

Wiki User

βˆ™ 14y ago

You do four things:

make sure there's enough excess capacity in the box to handle the extra load--normally there is
change the wire from 14 gauge to 12 gauge.
change the breaker from 15 amp to 20 amp
if the circuit has one outlet, change it from 15 amp to 20 amp.

This answer is:
User Avatar

User Avatar

Wiki User

βˆ™ 14y ago

Not a good idea. The only safe way it can be done is if by chance the wire from the 15 amp breaker is a #12 wire which is rated for 20 amps. The #14 wire which is most likely connected to the 15 amp breaker is only rated at 15 amps. By connecting a 20 amp possible load to a 15 amp rated circuit there is the possibility of heat being generated by the wire resulting in insulation failure and then circuit failure.

This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: Can a 15 amp breaker be replaced with a 20 amp?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Continue Learning about Natural Sciences

Does square D make a circuit breaker with a 15 amp and 20 amp breaker in the same breaker?

No tandem breakers are of the same value.


20 amp breaker power verse 15amp breaker power?

A 20 amp breaker can handle up to 20 amps of current before tripping, while a 15 amp breaker can handle up to 15 amps. This means the 20 amp breaker can support heavier electrical loads without tripping compared to the 15 amp breaker. It's important to match the breaker size to the electrical load to prevent overloading and potential hazards.


Can a 15 amp extension cord be plugged into a 20 amp breaker?

It is not recommended to plug a 15 amp extension cord into a 20 amp breaker because the extension cord may overheat and pose a fire hazard. It is safer to use a cord that matches the amp rating of the breaker to prevent potential electrical issues.


Can you use a double pole 15 amp breaker in place of a 20 amp single pole breaker for a 12000 BTU air conditioner?

No, it is not safe to use a double pole 15 amp breaker in place of a 20 amp single pole breaker for a 12000 BTU air conditioner. The breaker size must match the electrical requirements of the appliance to prevent overheating and potential fire hazards. It is recommended to consult with a qualified electrician to ensure the proper breaker is used.


Can you run a 20 amp machine on a 15 amp plug?

No, a 20 amp machine should not be run on a 15 amp plug because the plug is not designed to handle the higher electrical load of the machine. This could lead to overheating, tripping of the circuit breaker, or even starting a fire. It is important to always match the amp rating of the plug to the requirements of the machine.

Related questions

Can a 20 amp breaker be replaced with a 15 amp?

Yes, provided that you don't really need 20 A on the circuit.


Does square D make a circuit breaker with a 15 amp and 20 amp breaker in the same breaker?

No tandem breakers are of the same value.


20 amp breaker power verse 15amp breaker power?

A 20 amp breaker can handle up to 20 amps of current before tripping, while a 15 amp breaker can handle up to 15 amps. This means the 20 amp breaker can support heavier electrical loads without tripping compared to the 15 amp breaker. It's important to match the breaker size to the electrical load to prevent overloading and potential hazards.


Can a 15 amp extension cord be plugged into a 20 amp breaker?

It is not recommended to plug a 15 amp extension cord into a 20 amp breaker because the extension cord may overheat and pose a fire hazard. It is safer to use a cord that matches the amp rating of the breaker to prevent potential electrical issues.


Can you use a double pole 15 amp breaker in place of a 20 amp single pole breaker for a 12000 BTU air conditioner?

No, it is not safe to use a double pole 15 amp breaker in place of a 20 amp single pole breaker for a 12000 BTU air conditioner. The breaker size must match the electrical requirements of the appliance to prevent overheating and potential fire hazards. It is recommended to consult with a qualified electrician to ensure the proper breaker is used.


Should 25 amps breaker be replaced by 20 amps?

For typical residential house wiring 12 AWG wire is required for a 20 Amp breaker. If you change out the breaker for a 25 A breaker you would have to rewire the circuit with 10 AWG. In that case you could up the breaker to 30 Amps. All outlets and switches should be rated at the same voltage and current as the breaker.


What size breaker is needed for a 1100 watt microwave?

A minimum of 15-amp breaker is "needed", but a 20-amp is often required by electrical code for that situation.


Can you run a 20 amp machine on a 15 amp plug?

No, a 20 amp machine should not be run on a 15 amp plug because the plug is not designed to handle the higher electrical load of the machine. This could lead to overheating, tripping of the circuit breaker, or even starting a fire. It is important to always match the amp rating of the plug to the requirements of the machine.


Can you hook a 15 amp and 20 amp breaker to a breaker box using 20 amp wire?

No, you should use wire that matches the lowest amp rating of the breakers connected to it. In this case, you should use 15 amp wire since one of the breakers is a 15 amp breaker. Matching the wire gauge to the lowest amp rating ensures the wire is protected from overheating in case of a short circuit.


What is the wire size required for 1800 watts for lamps?

14 gauge will handle it with a 15 amp breaker. If you use 12 gauge use a 20 amp breaker.


Can a circuit breaker be tripped by using 20 amp sockets instead of 15 amp sockets?

A circuit breaker protects the wires that the devices are connected to. If the devices that are connected to the circuit are 20 amps the wire size should be #12 wire fed from a 20 amp breaker. This breaker should not trip unless the circuit is overloaded or a fault occurs on the circuit. If the devices that are connected to the circuit are15 amps the wire size should be #14 wire fed from a15 amp breaker. This breaker should not trip unless the circuit is overloaded or a fault occurs on the circuit. Putting 20 amp sockets on this 15 amp circuit will work but the circuit is limited to the amount of load that can be plugged in. You will not get the full capacity of the 20 socket because the breaker will trip at 15 amps.


Can a 20 amp breaker be replaced with a 30 amp if small window unit causes lights to dim when compressor kicks in?

No, the breaker is there to trip at 20 amps because the supply wiring can only supply 20 amps max at that point. So a larger breaker could give you a house fire.