Best Answer

It depends on the current flowing in the wire. V=IR. The wires have resistance (easily calculated, approx. .32 ohms for 200 feet of wire (100 feet out and back)). If 20 amps are flowing in the circuit the the voltage drop is about 6.4 volts. That means you're converting electricity to heat in the wires at a rate of about 130 Watts. If less current is flowing then there is a smaller voltage drop in the wire.

User Avatar

Wiki User

15y ago
This answer is:
User Avatar
More answers
User Avatar

AnswerBot

1mo ago

The voltage drop on a 14 2 wire over a 200-foot run will depend on the amperage of the circuit. For a typical residential 15-amp circuit, the voltage drop could be up to 9.6 volts. It is important to calculate the voltage drop to ensure proper functioning of the electrical equipment.

This answer is:
User Avatar

User Avatar

Wiki User

14y ago

Voltage drop would depend on the amperage draw of the device

This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: How much voltage drop will there be if you use 14 2 wire on a run of two hundred feet?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Continue Learning about Natural Sciences

How much loss from power pole to 200 amp breaker box then off 400 feet then split at a pump house then another 30 feet to a 100 amp breaker box?

The loss of voltage over a distance depends on factors such as wire gauge, current flowing, and resistance. For a 200-amp service at 400 feet and then branching off another 30 feet to a separate 100-amp service, there could be a noticeable voltage drop. It is recommended to consult with a licensed electrician to calculate the exact voltage drop and determine if any voltage compensation measures are needed.


What is voltage drop calculation?

Voltage drop calculation is a method used to determine how much the voltage decreases in an electrical circuit due to the resistance of the wires and components. It helps in ensuring that the voltage at the intended load is within the acceptable range for proper operation. This calculation is important to ensure that the voltage supplied to the load is sufficient for it to function correctly.


How much voltage drop will be in 6 meter length of 16 mm² copper wire for 40 Amp load?

The voltage drop in a 6-meter length of 16 mm² copper wire carrying a 40 Amp load can be calculated using Ohm's Law and the wire's resistance. Copper wire has a resistance of about 0.000133 ohms per meter. The voltage drop can be found using the formula Voltage Drop = Current x Resistance x Length. Therefore, the voltage drop in this scenario would be approximately 0.32 volts.


How much does amperage drop with distance?

Amperage drop with distance depends on the resistance of the conductor and the load. As distance increases, resistance increases, leading to higher voltage drop. This can result in lower amperage at the end of the circuit compared to the source. Use Ohm's Law (V=IR) to calculate the amperage drop based on the resistance and distance.


How much voltage loss with a dimmer switch when used for lights?

The voltage loss from using a dimmer switch varies depending on the type of dimmer and the settings used. In most cases, a standard dimmer switch can introduce a voltage drop of around 5-20% when dimming the lights. This reduction in voltage helps regulate the amount of current flowing to the light fixture, allowing for variable brightness levels.

Related questions

How much is 100 feet?

A hundred feet of what?


What are 2 advantages for this particular control voltage?

With voltage control there is so much voltage drop due to resistor, that's the disadvantage


Why is the peak voltage not exactly equal to the peak voltage of the alernating voltage and by how much it differ?

If you are referring to the voltage after the rectifiers in a powersupply, it is due to the voltage drop across the rectifiers.


Whats the permissible voltage drop in a 240V system?

You shouldn't really have much voltage "drop". If you do, it usually means that there is a poor connection somewhere along your service line or inside wiring. Any significant amount of voltage drop can mean that you are at risk of a fire. On the other hand, line voltage into a house may not actually be 240 VAC. Measure the ACTUAL voltage with everything turned off, then see where it goes when you start turning things back on. The difference between the supplied voltage and the load voltage is the voltage "drop".


I have a 5000 watt Honda generator. How much of a voltage drop will a 25 foot portable generator cord cause?

A 25 foot cord will not cause enough voltage drop to worry about.


How much high voltage cable is there on a reel?

300 feet


How much voltage is there between your head and feet?

200 ~300 V


How much feet is 400 feet per second?

Must be close to four hundred....


How much wire in a car?

Probably a couple of hundred feet.


How much does a 308 caliber drop at 600 yards?

About 4 feet


How much loss from power pole to 200 amp breaker box then off 400 feet then split at a pump house then another 30 feet to a 100 amp breaker box?

The loss of voltage over a distance depends on factors such as wire gauge, current flowing, and resistance. For a 200-amp service at 400 feet and then branching off another 30 feet to a separate 100-amp service, there could be a noticeable voltage drop. It is recommended to consult with a licensed electrician to calculate the exact voltage drop and determine if any voltage compensation measures are needed.


How much is one hundred forty seven and nine hundred twenty three millionths inches?

026 feet