Best Answer

1 # 10 hot

1 # 12 neutral

1#12 ground

User Avatar

Wiki User

12y ago
This answer is:
User Avatar
More answers
User Avatar

AnswerBot

6mo ago

For a 250-foot run, it is recommended to use a wire gauge that is appropriate for the electrical load and voltage requirements of the circuit. Typically, for longer runs like this, a thicker gauge wire such as 10 AWG or 12 AWG may be used to minimize voltage drop and ensure proper current flow. It is important to consult local electrical codes and regulations to determine the specific wire type and gauge suitable for your application.

This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: What wire do you use for 250 foot run?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Continue Learning about Natural Sciences

Can I run a 230 volt 20 amp table saw on 10 3 with a 250 foot run?

It is not recommended to run a 230 volt 20 amp table saw on a 10/3 wire with a 250-foot run. A longer wire run may result in voltage drop that could potentially damage the saw or cause it to operate inefficiently. It is advisable to consult with an electrician to determine the appropriate wire size for the distance involved.


What size wire for 200 amp service with a 60 foot run?

For a 200 amp service with a 60 foot run, it is recommended to use 3/0 AWG copper wire or 250 kcmil aluminum wire to ensure proper voltage drop and capacity for the load. Be sure to consult with local codes and a licensed electrician for specific requirements and installation guidance.


Can you run a 10 gauge wire 250 feet to the barn on a 120 amp breaker in the house If not what amp breaker should I use?

#10 cable is no good for 120 amps, you need #2 cable, and it can be used at a distance of 250 ft.


What size wire for 250 foot extension cord to run a 120 Volt 8 amp electric tree trimmer?

For a 5% volt drop of 6 volts the total resistance should be less than 6/8 ohms, 0.75 ohms, which for a total wire run of 500 ft is equivalent to 1.5 ohms per 1000 ft. Wire tables show that a #10 cable should be used. A #12 cable would give a volt drop of 5.3% which would probably be acceptable for occasional use and easier to store.


What size wire for 80 amp breaker with a hundred foot run?

For an 80 amp breaker with a one hundred foot run, you would typically need to use 4 AWG copper wire to minimize voltage drop and ensure safe operation of the circuit. It is important to consult with a qualified electrician to determine the specific requirements for your installation based on local codes and conditions.

Related questions

Can I run a 230 volt 20 amp table saw on 10 3 with a 250 foot run?

It is not recommended to run a 230 volt 20 amp table saw on a 10/3 wire with a 250-foot run. A longer wire run may result in voltage drop that could potentially damage the saw or cause it to operate inefficiently. It is advisable to consult with an electrician to determine the appropriate wire size for the distance involved.


What size wire for 200 amp service with a 60 foot run?

For a 200 amp service with a 60 foot run, it is recommended to use 3/0 AWG copper wire or 250 kcmil aluminum wire to ensure proper voltage drop and capacity for the load. Be sure to consult with local codes and a licensed electrician for specific requirements and installation guidance.


Can you run a 10 gauge wire 250 feet to the barn on a 120 amp breaker in the house If not what amp breaker should I use?

#10 cable is no good for 120 amps, you need #2 cable, and it can be used at a distance of 250 ft.


What size wire for 250 foot extension cord to run a 120 Volt 8 amp electric tree trimmer?

For a 5% volt drop of 6 volts the total resistance should be less than 6/8 ohms, 0.75 ohms, which for a total wire run of 500 ft is equivalent to 1.5 ohms per 1000 ft. Wire tables show that a #10 cable should be used. A #12 cable would give a volt drop of 5.3% which would probably be acceptable for occasional use and easier to store.


What size service head is needed to power 250 amp 415 volt installation?

If you use 250 or 300 MCM wire you will need a 2 1/2" weather head. If you use 300 MCM wire then you will need a 3" weather head.


What size wire for 80 amp breaker with a hundred foot run?

For an 80 amp breaker with a one hundred foot run, you would typically need to use 4 AWG copper wire to minimize voltage drop and ensure safe operation of the circuit. It is important to consult with a qualified electrician to determine the specific requirements for your installation based on local codes and conditions.


How do you use hop in a sentence?

He tried to hop over the wire, but he caught his foot and tripped.


What size wire is needed for 6.3 amps 240 volts 50 foot run?

For a 50-foot run with a 6.3-amp load at 240 volts, you can use 14-gauge wire as it can safely handle up to 15 amps. If you want to take into account voltage drop for longer runs, you may opt for even thicker wire like 12-gauge to minimize power loss. It's always a good idea to consult with a professional electrician for accurate recommendations.


What gauge wire is used to run smoke detectors?

14-3 Is the standard wire use for residental smoke detectors.


Can you use a 62 wire to run a 240volt 60 amp circuit in the USA?

no


Do you have to use copper for entire run of water line from street to my house It's a 1000 foot run and will be really expensive if I have to?

Use PVC pipe


What size wire and circuit breaker is needed for an electric oven 4 wires with rated load of 34.9 amps 220v that is about 100 foot run from the electrical panel?

That would be a 40 amp 220v circuit. Circuit breaker is 40 amps and wire is 8 awg. Should use solid copper wire. Follow oven installation instructions.