You cannot convert 2.6 kw to amps with that information only.
In order to convert watts to amps, you also need to know either current or voltage. This is because watts is volts times amps, and volts is current times resistance
I=amps, P=power(watts), E=volts I=P/E
I=2600/208
I=12.5 amps
Divide the watts by the volts, so it's 2600/220 for a basic answer. If the power factor is less than 1 the current is more, maybe 30% more in a typical case.
Divide 2600 watts by 220 volts, answer is in amps.
The formula you are looking for is I = W/E. Amps = Watts/Volts.
The equation that you are looking for is I =W/E. Amps = Watts/Volts. To change kW to watts multiply by 1000.
The equation that you are looking for is I = W/E. Amps = Watts/Volts. To change 2.6 kW to watts multiply the 2.6 kW by 1000 and then use the equation.
The formula you are looking for is I = W/E. Amps = Watts/Volts.
50 Amps Single Phase 20 Amps Three Phase
depends what the source voltage isone horsepower equals to 746watts (assuming 100% efficiency)746 watts divided by voltage source equals current (amps)AnswerIn countries, such as the USA, where the horsepower is still used as a means of measuring power, it is always used to measure the output power of a motor.So, in order to determine the current drawn by the motor, you will first need to find out its input power. The input power is the output power divided by the machine's efficiency. Once you know its input power, then you can find its current by dividing the input power by the supply voltage. In practise, you will need to use a wattmeter to determine its input power.
for three phase the calculation is 30,000 = 1.73*V*I - simple as that. For single Phase the calculation is 30,000 = V*I - simple as that It is important to note the voltage in the first line is Line to Line (typically how it is specified in three phase power systems), and the second line it is Line to neutral. A 30KVA transformer is the same as 30,000VA to find out the Amps you need to divide the voltage if the transformer is single phase for example: 30,000VA / 480V = 62.5 Amps The calculation for a 3 phase transformer is the VA / voltage / 1.73 for example: 30,000VA /480V / 1.73 = 36.12 Amps
use 1.0 as your PF Understand that K=1000, so KVA simply means thousands of volts times amps. First, multiply KVA by 1000 to get VA, then divide by the voltage of the system to get amps. Example: 6KVA, 240V single-phase. 6 * 1000 = 6000 VA 6000 / 240 = 25A
For a single phase circuit, the equation you are looking for is I = W/E. Amps = Watts/Volts.
500,000 watts/240 volts = 2,083.34 Amps (single phase)
The equation that you are looking for is Amps = Watts/Volts. There are 6000 watts in 6kW.
The formula you are looking for is I = W/E. Amps = Watts/Volts.
The formula you are looking for is , A = kva x 1000/Volts.
75 Amps theoretically Need to know if the generator is 3 phase or single phase.
For a single phase 3 HP motor at 208 volts the amperage is 18.7 amps. For a three phase 3 HP motor at 208 volts the amperage is 10.5 amps. This figure is derived at by taking the full load amps at 230 volts and adding 10%. As the voltage goes down the amperage goes up. For 200 volt motors 15% is added to the FLA of a 230 volt motor.
50 Amps Single Phase 20 Amps Three Phase
At 240v single phase it's 70.8 amps. If it runs on 2 wires plus ground, take the voltage rating of the equipment and divide that into the watts to get amps. At 480v 3 phase it's 25.8 amps. At 208v 3 phase it's 47.2 amps. <<>> There are zero amps in 14 kW. A voltage needs to be stated. I = W/E, Amps = Watts/Volts.
It depends on the voltage of the motor, and whether it is single-phase or 3-phase. A 120 VAC 2HP single phase motor draws almost 20 amps, a 240 VAC single-phase 2HP motor draws about 10 amps. A 480 VAC 2HP three-phase motor only draws about 6 amps.
Rephrase your question, as it doesn't make any sense. If the primary side of the transformer is 480 volts 3 phase, this transformer can be supplied from a breaker as big as 180 amps. If 480 volts 3 phase is your secondary then you can supply up to 180 amps to your loads.
Assuming it is a 208-volt line voltage (as normal in 3-phase) the phase voltage is that divided by sqrt(3), or 120 volts. Each phase has to supply 10 kW so the current on each phase is 83.3 amps.