NEC Table 310.16 says you will need #6 copper, with a decent insulation on it, like THHN,
or # 4 Aluminum, again with good insulation.
Indoors - Article 680.43(A) says you will need one more regular outlet within 6-10 ft from the tub or spa, if it is "indoors". This must be on a GFI.
ALL metal parts of everything must be bonded. - that's a simple restatement of several sub-paragraphs.
Have fun!!
That will be in your electric wiring regulations, see an electrician if you don't know.
<<>>
A #8 copper conductor with an insulation factor of 90 degrees C is rated at 55 amps. If the spa operates at a continuous rating the feeder conductor has to be calculated at 80% capacity. 55 x .8 = 44 amps. If the spa was mine I would use a #6 copper conductor with an insulation rating of 90 degrees C which is rated at 75 amps. De rated by 80% will give it a working amperage of 60 amps. Using a larger size wire also gives you a longer distance to place the spa from the distribution panel with out having voltage drop enter into the equation. Don't forget that a ground fault device needs to be in the circuit that supplies a spa or hot tub.
4
Look to see if the 30 amp panel is fed with a two wire or a three wire. If it is a two wire then you are out of luck. If the panel is fed with a three wire then the panel should have the neutral terminated in the panel. It is this neutral that you need for 120 volt connections. You didn't state how many panel slots there are in the panel. If you are able install a 15 amp breaker into the panel and connect the wires going to the load. The black wire will go to the breaker and the white wire will go to the neutral bar in the panel.
I don't know if you are trying to ask if you can run a 240V panel off a GFCI or run a 120 V sub panel off of a GFCI. Can you clarify please,,,Thanks
You need a 3 conductor wire with ground. For example if you had a 30 amp breaker for that outlet you would need 10awg 3w/ground. That's 10 gauge 3 conductor with ground and replace the old wire back to the panel.
That could only happen if the neutral wire (white) becomes disconnected at either the panel, the meter base or the transformer.
I suspect you mean GFIC breaker. The dryer will not cause the breaker to fail.
Look to see if the 30 amp panel is fed with a two wire or a three wire. If it is a two wire then you are out of luck. If the panel is fed with a three wire then the panel should have the neutral terminated in the panel. It is this neutral that you need for 120 volt connections. You didn't state how many panel slots there are in the panel. If you are able install a 15 amp breaker into the panel and connect the wires going to the load. The black wire will go to the breaker and the white wire will go to the neutral bar in the panel.
you should have three wires into the panel. two of them go to the double breakers or pull switch and the last is the ground lead. You can pick up 110 vac from one side of either breaker and that ground connection. DO NOT connect to the both breaker wires as that will be 220 vac
I don't know if you are trying to ask if you can run a 240V panel off a GFCI or run a 120 V sub panel off of a GFCI. Can you clarify please,,,Thanks
You need a 3 conductor wire with ground. For example if you had a 30 amp breaker for that outlet you would need 10awg 3w/ground. That's 10 gauge 3 conductor with ground and replace the old wire back to the panel.
That could only happen if the neutral wire (white) becomes disconnected at either the panel, the meter base or the transformer.
I suspect you mean GFIC breaker. The dryer will not cause the breaker to fail.
You can't.
Answer for USA, Canada and countries running a 60 Hertz supply service.One 240 volt receptacle fed from a two pole breaker from the distribution panel. The size of the breaker is determined by the load current and the wire sized accordingly.
Move things around until you have space for a double-pole breaker, which is required for 240V. Don't be stupid and connect 2 separate breakers in non-adjacent positions. It might work, and then again it might fry something too.
In America, a 2-pole breaker is controlling 240V. 120V per leg.
Absolutely not. #2awg conductors are only good for about 100 amps depending on Cu or al. see nec table 310-16.
Yes it will operate it fine.