Conductors should not be smaller than #8 copper. With that that in mind a 1" conduit would work. Better to use at least 1 1/2-2" depending on the amps of your service. Bigger is always better!
<><><>
As always, if you are in doubt about what to do, the best advice anyone should give you is to call a licensed electrician to advise what work is needed.
Before you do any work yourself,
on electrical circuits, equipment or appliances,
always use a test meter to ensure the circuit is, in fact, de-energized.
IF YOU ARE NOT ALREADY SURE YOU CAN DO THIS JOB
SAFELY AND COMPETENTLY
REFER THIS WORK TO QUALIFIED PROFESSIONALS.
100 amps
When 2 #12 THW, 3 #10 THW, and 3 #8 THW conductors are installed together in the same conduit, what minimum size conduit must be used for these conductors
4 inch rigid conduit
Three number three wires can be installed in an inch and one quarter conduit.
They can be either separated or combined. What governs the choice is the size of the service and the conductors feeding the service and the ability to physically connect metering equipment to larger size conduits. When paralleling conduits make sure all the phase wires are in their individual conduits to cancel the field effect of the wires. Eg. conduit 1 - L1 + L2 + N , conduit 2 - L1 + L2 + N. Likewise with three phase, conduit 1 - L1, L2, L3, conduit 2 L1, L2, L3.
The sizing of conduit systems that wire has to be pulled into is dependant on the physical size of the conductor being drawn into the conduit. The second governing factor is the conductor count of the specific conductor that is needed. A 500 MCM copper conductor with an insulation factor of 90 degrees C is rated at 430 amps. This is where the conductor count is need by the service, as to whether the service is single or three phase. In this specific case, the electrical code will allow both single and three phase installations to use the same size conduit. A maximum total of four 500 MCM conductors can be drawn into a 78 mm diameter conduit.
It's called a Weatherhead.
250 MCM aluminum minimum
4 inch rigid conduit
4 inch rigid conduit
Three number three wires can be installed in an inch and one quarter conduit.
No, the conduit has to be supported individually from a supportive structure. The spacing of the strapping is related to the size of the conduit.
If the service stack is supported by a support structure and the utility feed drop is not supported from the conduit, the size of the conduit can be 1 1/4". If the service stack is used to support the utility feed drop then the conduit has to be 2" schedule 40 conduit. The reasoning behind this is that if in a storm a tree limb falls across the service drop, the lighter weight conduit could bend and pinch the wires in the stack and short out. This would be ahead of the main service breaker and the only protection for the wire would be the primary fuse at the transformer. Theoretically this amperage could rise to 50000 amps before the primary fuse blows. A schedule 40 service stack if supported, as the code requires, will withstand most tree falls. What is most likely to happen is that the utility connectors will pull apart leaving the service stack intact.
They can be either separated or combined. What governs the choice is the size of the service and the conductors feeding the service and the ability to physically connect metering equipment to larger size conduits. When paralleling conduits make sure all the phase wires are in their individual conduits to cancel the field effect of the wires. Eg. conduit 1 - L1 + L2 + N , conduit 2 - L1 + L2 + N. Likewise with three phase, conduit 1 - L1, L2, L3, conduit 2 L1, L2, L3.
The sizing of conduit systems that wire has to be pulled into is dependant on the physical size of the conductor being drawn into the conduit. The second governing factor is the conductor count of the specific conductor that is needed. A 500 MCM copper conductor with an insulation factor of 90 degrees C is rated at 430 amps. This is where the conductor count is need by the service, as to whether the service is single or three phase. In this specific case, the electrical code will allow both single and three phase installations to use the same size conduit. A maximum total of four 500 MCM conductors can be drawn into a 78 mm diameter conduit.
250 mcm
Please be more specific about 'service'.
Actual hole size for 1 inch conduit is 1.362"
50 mm or 2 inch will handle the 3/0 wires for a 200 amp service.