Can I install a 10 amp Wayne 3/4 HP sump pump on an existing dedicated 15 amp circuit with 14 ga wiring? I just installed a Wayne 1/2 hp (replacing a failed 1/3 HP) and think I might need more as my discharge run is 125 feet even though the lift is only 2 ft... all underground
This question has been moved to the discuss question page, leave it up for a week.
The circuit breaker is sized by the amperage of the load. Keep in mind that the motor load circuit wire size has to be sized for 125% of the motors full load amperage. And the motors circuit breaker is usually sized at 250% of the motors full load amperage.
The sizing of the circuit breaker and hence the wire size to feed the pump are all dependant upon the amperage of the pump. This question can not be answered without that information.
Depends entirely on the voltage and current rating of your pump.
Usually 30 Amp 240 volts, but there will be a spec on the well pump.
When installing a circuit breaker, you size the breaker based on the wire size. The breaker should be matched to the ampacity of the wire to ensure proper protection against overloads and short circuits. The device being controlled by the breaker is not a determining factor in sizing the breaker.
You use the correct size breaker depending on the size wire in the circuit. If the circuit is wired with AWG #12 wire use a 20 amp breaker. If it is wired with AWG #14 wire then use a 15 amp breaker.
The sizing of the circuit breaker and hence the wire size to feed the pump are all dependant upon the amperage of the pump. This question can not be answered without that information.
Depends entirely on the voltage and current rating of your pump.
Usually 30 Amp 240 volts, but there will be a spec on the well pump.
Branch circuits are protected by the circuit breaker found in the electrical panel. Each circuit should have its one breaker. The breaker should be rated to protect the insulation of the wire, so you can determine the breaker size based on the circuit conductor size Example #14-2 should be protected by a 15 amp breaker
When installing a circuit breaker, you size the breaker based on the wire size. The breaker should be matched to the ampacity of the wire to ensure proper protection against overloads and short circuits. The device being controlled by the breaker is not a determining factor in sizing the breaker.
You use the correct size breaker depending on the size wire in the circuit. If the circuit is wired with AWG #12 wire use a 20 amp breaker. If it is wired with AWG #14 wire then use a 15 amp breaker.
A 15 amp dedicated circuit breaker should be used for the dishwasher. The disposal can be wired to the general kitchen 15 amp circuit.
Depends on how many amps it pulls and the size of the wire in the circuit.
The pool light is usually on a 15 amp circuit. The breaker feeding this circuit must have a GFCI rating.
For an accurate calculation it will be necessary to know what the size of breaker exists in the pump house and what size conductors are used. Power loss is measured using actual amps required, not size of the circuit involved. But the size of circuit (breaker size) can be used. Voltage must also be known.
The size breaker you use is determined by the size wire used in the circuit. If you use AWG #12/2 wire then use a 20 amp breaker. If you use AWG # 14/2 then use a 15 amp breaker.
A circuit breaker protects the wires that the devices are connected to. If the devices that are connected to the circuit are 20 amps the wire size should be #12 wire fed from a 20 amp breaker. This breaker should not trip unless the circuit is overloaded or a fault occurs on the circuit. If the devices that are connected to the circuit are15 amps the wire size should be #14 wire fed from a15 amp breaker. This breaker should not trip unless the circuit is overloaded or a fault occurs on the circuit. Putting 20 amp sockets on this 15 amp circuit will work but the circuit is limited to the amount of load that can be plugged in. You will not get the full capacity of the 20 socket because the breaker will trip at 15 amps.