To calculate an answer a voltage must be stated.
It is not the number of bulbs that you worry about. It is the wire size that is your concern. If the circuit is wired with AWG 12/2 wire then use a 20 amp breaker. If it is wired with a AWG 14/2 wire then use a 15 amp breaker. You are protecting the wiring with the correct size breaker.
This formula will give you the amperage I = kw x 1000/1.73 x E x pf (pf = power factor). Take the amperage and multiply it by 125%. This will give you the breaker size that you need.
A breaker is sized by the wire size. The wire is sized by the amperage. The formula for amperage is I = W/E. Amps = Watts/Volts. As you can see with no voltage stated an answer can not be given.
Depends on the wire size you are using. If the generator breaker is a 30 amp then install a 30 amp breaker.
Usually 30 amp
50amp but if considering the breaker cannot withstand starting current you need to size the breaker up.
For a 30 amp breaker, you will need a wire that is at least 10 gauge in size.
For a 50 amp breaker, you will need a wire that is at least 6 gauge in size to safely handle the electrical load.
For a 50 amp breaker, you would typically need a 6-gauge wire.
6
8 AWG is typical.
To determine the size of the breaker needed for a 78 amp range, you typically need to use a breaker that is the next size up from the amp rating. This means that you would need an 80 amp breaker to safely accommodate the 78 amp range. However, always consult with a qualified electrician to ensure the correct breaker size for your specific electrical setup.
It is not the number of bulbs that you worry about. It is the wire size that is your concern. If the circuit is wired with AWG 12/2 wire then use a 20 amp breaker. If it is wired with a AWG 14/2 wire then use a 15 amp breaker. You are protecting the wiring with the correct size breaker.
This formula will give you the amperage I = kw x 1000/1.73 x E x pf (pf = power factor). Take the amperage and multiply it by 125%. This will give you the breaker size that you need.
When installing a circuit breaker, you size the breaker based on the wire size. The breaker should be matched to the ampacity of the wire to ensure proper protection against overloads and short circuits. The device being controlled by the breaker is not a determining factor in sizing the breaker.
You will need to use #8 wire.
A breaker is sized by the wire size. The wire is sized by the amperage. The formula for amperage is I = W/E. Amps = Watts/Volts. As you can see with no voltage stated an answer can not be given.