To answer this question the wattage of the heater is needed.
Yes, a 30 amp double pole breaker would be suitable for a 4800 watt wall heater. Since watts equals volts multiplied by amps, this wall heater on a 240-volt circuit would draw 20 amps (4800 watts/240 volts), which is less than the 30 amp capacity of the breaker.
To install an ATMOR instant water heater, first shut off the water supply and electric power. Mount the unit securely on a wall using the provided hardware. Connect the water pipes and electrical wires according to the manufacturer's instructions. Test the unit for proper operation before use.
Converting a natural gas heater to propane gas usually involves changing the orifice size and adjusting the gas pressure. It's important to consult the manufacturer's instructions or hire a professional to ensure the conversion is done safely and properly. Using the wrong type of gas can be dangerous and damage the heater.
Yes heater vents can be painted the same colour as your walls.
It is not recommended to install a gas heater next to an electric panel due to safety concerns. The heat generated by the gas heater could potentially affect the electrical components or create a fire hazard. It is best to consult a professional to determine the safest and most appropriate location for a gas wall heater.
There is a thermostat somewhere, usually on the wall or on the heater itself. Just turn the breaker off at the breaker box. Label the breaker if it is not already labeled. Once the power is turned off to the unit, you can disconnect the wires inside the heater to permanantly shut down the unit.
The breaker you use is determined by the size of the wire in the wall not by what is being connected to that circuit. If you have 14/2 wire then use a 15 amp breaker. If you have 12/2 wire then use a 20 amp breaker. The breaker protects the wiring not the item connected.
they generaly have a thermostat mounted on the unit or on the wall.
Yes, a 30 amp double pole breaker would be suitable for a 4800 watt wall heater. Since watts equals volts multiplied by amps, this wall heater on a 240-volt circuit would draw 20 amps (4800 watts/240 volts), which is less than the 30 amp capacity of the breaker.
To turn on a wall heater, locate the power switch or dial on the unit and set it to the desired temperature. Wait a few moments for the heater to start producing heat. Make sure the area around the heater is clear and not obstructed.
The breaker you use is determined by the size of the wire in the wall not by what is being connected to that circuit. If you have 14/2 wire then use a 15 amp breaker. If you have 12/2 wire then use a 20 amp breaker. The breaker protects the wiring not the item connected.
To effectively remove a baseboard heater from a room, first turn off the power to the heater at the circuit breaker. Then, remove the cover panel and disconnect the electrical wires. Next, unscrew the heater from the wall and carefully lift it out. Finally, patch up any holes left in the wall and dispose of the heater properly.
Installing a wall-mounted heater and AC unit in a room provides efficient heating and cooling, saves space, improves air circulation, and allows for precise temperature control.
To turn on a wall heater, locate the power switch or dial on the unit and set it to the desired temperature. Wait a few minutes for the heater to warm up and start producing heat. Make sure the area around the heater is clear and safe.
To effectively remove a baseboard heater, first turn off the power to the unit. Then, remove the cover and disconnect the electrical wiring. Next, unscrew the unit from the wall and carefully lift it out. Finally, patch up any holes left in the wall from the removal.
form_title=Wall Heater Repair form_header=8273 How would you best describe the problem?*= () No heat in one location () No heat in all locations () Excessive vibration (fan unit only) () Burning smell () Fluctuating heat () Thermostat not functioning properly Which kind of electric wall heating needs to be repaired?*= () Baseboard style () Wall fan unit
It is possible that the circuit breaker for the compressor unit is thrown (switched to "off"). Go outside to the compressor unit and follow the big cable up to the circuit breaker panel on the wall. If it is off, throw the switch to "on." If that is not the problem, something is probably wrong with the compressor unit. Turn off the breaker panel and call a repairman.