Best Answer

This reading must have been taken off of the distribution panel's main neutral conductor. The neutral conductor of a distribution panel carries the unbalanced current. If a panel is perfectly balanced there will be zero current on the neutral conductor. With loads being applied and removed from the distribution panel as equipment is turned on and off the neutral current will change. If the breaker that you turn off while the panel is in perfect balance when it is on, when it is turned off, it will put the panel into an unbalanced condition again and this is the current that you will be reading.

This is the reason that the electrical code allows a reduced neutral conductor size on distribution calculations. On engineered projects the circuit must be connected to the correct breaker position as shown on the electrical blueprint, as the engineer has already calculated the loads to produce the lowest possible current on the systems neutral conductor.

User Avatar

Wiki User

8y ago
This answer is:
User Avatar
More answers
User Avatar

AnswerBot

8mo ago

The increase in neutral amps after shutting off the breaker could be due to a phenomenon called neutral leakage. This occurs when there is an unbalanced load on the phases, causing some current to flow through the neutral even when the breaker is off. It may also indicate a fault in the electrical system that needs to be investigated by a professional.

This answer is:
User Avatar

User Avatar

Wiki User

9y ago

Something is wrong. If you're talking about the neutral for that particular circuit and it's a 120 volt circuit then the neutral should be 0 when breaker is off.

This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: Why does Neutral amps increase after shutting off breaker?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

What's a double breaker 20 amps and 30 amps?

A double breaker is a breaker that has 2 switches on it. One of the switches is 20 amps and the other is 30 amps.


Is it necessary to balance a house fuse panel to save electricity and if so why and how is it done?

A balanced house panel should be the ultimate goal. It will not save you electricity as the watt meter on the house monitors the use of power from both legs of the incoming power. To balance a panel you want the current from L1 to Neutral to equal L2 to Neutral. The neutral carries the unbalanced current between L1 and L2. A perfectly balanced panel will have no current on the neutral. It is done by knowing what the current draw is on every breaker. Then they are physically positioned so that they equal each other on the opposite leg. e.g. breaker 1 on leg L1 = 5 amps, breaker 2 on leg L2 = 10 amps, breaker 3 on leg L1 = 10 amps, breaker 4 on leg L2 = 5 amps. Total up all amperages on L1 and then on L2 , if they are equal then the panel is balanced with no current on the neutral.


What is KA in Circuit Breaker?

KA stands for kilo-amps, or thousands of amps. Thus a 2KA breaker means it will trip when the load exceeds 2,000 amps.


What is the maximum amperage capacity of a Siemens breaker that is rated at 200 amps?

The maximum amperage capacity of a Siemens breaker rated at 200 amps is 200 amps.


What is the maximum current rating for the circuit breaker, rated at 150 amps?

The maximum current rating for the circuit breaker is 150 amps.


What is the maximum current rating for a 2 pole breaker that can handle 25 amps?

The maximum current rating for a 2 pole breaker that can handle 25 amps is 25 amps.


What is the purpose of a 15 amp double breaker in an electrical circuit?

A 15 amp double breaker in an electrical circuit is designed to protect the circuit from overloading by shutting off the power if the current exceeds 15 amps. This helps prevent overheating and potential fire hazards in the wiring.


If a breaker is rated for 30 amps and is 2 poles is it ok to put an appliance that draws 50 amps?

The number that is on a breaker is the amount of amperage that the breaker can deliver before it trips. This is the same regardless of how many poles the breaker is.


What is type of breaker for 41 amp's?

For a 41 amp load, you would typically use a 50 amp circuit breaker. The general rule is to select a breaker size that is 125% of the continuous load amps or equal to the load amps if it is not a continuous load. In this case, 41 amps is considered a continuous load, so you would round up to the nearest available breaker size, which is 50 amps.


What is 6InA in circuit breaker?

61 nano-amps is 0.061 milliamps or 0.000061 amps


What is the maximum current capacity of the circuit breaker rated at 150 amp?

The maximum current capacity of a circuit breaker rated at 150 amps is 150 amps.


What breaker to use in a bedroom that holds up to 15 amps with 120v?

15 amp breaker.