answersLogoWhite

0


Best Answer

No, there is a tandem single pole 3030 but GE does not make a tandem two pole 3030.

User Avatar

Wiki User

10y ago
This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: Does GE make a tandem two pole 30 - 30 amp breaker?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

Does square D make a circuit breaker with a 15 amp and 20 amp breaker in the same breaker?

No tandem breakers are of the same value.


Does a 15 amp tandem breaker equal 30 amps total?

No, each segment of a tandem breaker is what the breaker rating on the handle states. Tandem breakers are used when there is no space left in the distribution panelboard. You get an extra circuit by removing the full size breaker and installing a tandem breaker,


Does a double 50 amp breaker make a 100 amp?

No, a double pole 50 amp breaker protects a 240 volt supply at 50 amps. The number that is on the handle of the breaker is the amperage that the breaker will trip at if an overload occurs on the circuit.


Is a double throw 15amp breaker the same as a 30 amp breaker amp?

You have a double pole breaker for 240Volt supply. The maximum current is 15 amp.


What amp breaker for 12-2?

AWG 12/2 requires the use of a 20 amp single pole breaker.


Is a 2 pole 30 amp circuit breaker equivalent to 30 amp?

Yes.


Will a 2 pole 60 amp ITE Gould or Westinghouse breaker replace a 2 pole 60 amp T and B unit?

If the breaker will snap on the bus bar, yes.


What type of appliance would be use a two pole 50 amp breaker?

In North America this size breaker could be used on a welding machine. A range in the home would use a 40 amp two pole breaker.


Can you use a double pole 15 amp breaker in place of a 20 amp single pole breaker for a 12000 BTU air conditioner?

If the 12,000 BTU A/C only requires 20 amps to run then yes you can use the same 12 gauge wire but you cannot change it to a 15 amp breaker. You will need to install a 20 amp double pole breaker. If it requires more than 20 amps you will have to replace the wiring and breaker.


Can you use two 15 amp single pole breakers in place of a double pole 30 amp breaker?

Yes. An everyday occurrence of this circuitry is in your kitchen counter split receptacles. The top half of the receptacle is a 15 amp circuit and from the same breaker the bottom half of the receptacle is another 15 amp circuit. A two pole single handle breaker is a common trip. If one of the circuits fed from the breaker faults the other connected circuit will shut off also. If you are talking about slot position in a breaker panel, you can remove the two pole breaker and install two single pole breakers.


What size breaker to use for a hand dryer its 120v 20amps?

Single pole 20 amp breaker.


What is breaker size for 240 volt 9 KW?

The formula you are looking for is I = W/E.