What is the largest size of sub-panel and wire that should be used from a 200 amp service for a basement apartment?

Sorry, it depends ...

Literally, it is a question of which manufacturer's load center the sub-panel is being derived from.

Some manufacturers, Square D [QO line] for example, have a 200 amp breaker, QO2200BB, that can be installed in the panel as a branch breaker. This would theoretically allow you to install a 200 amp sub-panel in the apartment.

You need to calculate the load for the apartment and size your branch breaker accordingly.

Remember that the neutral has to be isolated from the ground buss in the sub-panel.

<><><>

As always, if you are in doubt about what to do, the best advice anyone should give you is to call a licensed electrician to advise what work is needed.

Before you do any work yourself,

on electrical circuits, equipment or appliances,

always use a test meter to ensure the circuit is, in fact, de-energized.

IF YOU ARE NOT ALREADY SURE YOU CAN DO THIS JOB

SAFELY AND COMPETENTLY

REFER THIS WORK TO QUALIFIED PROFESSIONALS.

User Avatar

Wiki User

โˆ™ 2009-08-09 07:04:15
This answer is:
๐Ÿ™
0
๐Ÿคจ
0
๐Ÿ˜ฎ
0
User Avatar

Add your answer:

Earn +20 pts
Q: What is the largest size of sub-panel and wire that should be used from a 200A service for a basement apartment?
Write your answer...
Submit
Related questions

Can a family of six have six service animals in an apartment?

Whether or not a family of six can have six service animals in an apartment will depend upon the particular apartment in question. The apartment must have enough space for the animals to not be overcrowded.


Where can rent apartment in Baltics?

You can rent apartment in Baltics through online service: http://bookapartment.eu


How do I find a low income apartment in brooklyn?

I would suggest using an apartment locator service. Apartment locators find apartments for you and pay you for it.


Do you need a broker license to operate a apartment locating service?

no!


100 amp subpanel from 200amp service what size wire do you use?

A #3 copper wire with insulation rating of 90 degrees C has an amperage rating of 105 amps.


Do you need a grounding rod at a subpanel on a detached building?

Yes. The panel must be grounded with its own grounding rod. The ground will not be provided with the feeders to the panel, these will only contain your phase wires and neutral. Also make sure that any subpanel installed does not have the neutral bonded to ground. This should only be done at the main panel where the electrical utility service is connected.


Who do residents complain to about poor service in apartment servicing?

They can complain to the apartment management staff. If this produces no results then they can complain to the Code Enforcement Bureau.


Who is the largest Wireless Internet Service Provider in America?

Verizon is the largest Wireless Internet Service Provider in America


What services does Basement Technologies offer?

The company Basement Technologies provides basemnt waterproofing services. They also offer fundation wall replacements and provide their service in the US and Canada.


What is the largest branches of the military?

The US Army is the largest branch of service.


What is largest online service?

google


Can I get high speed cable internet service in an apartment?

You can get cable Internet in an apartment. Just call your cable company and tell them what you want. They'll fix you up.


Largest aircraft in service today?

The Airbus A380 is the largest passenger aircraft.


Is it unsafe to have 60A service going into a new electrical box designed for 100A?

Its not recommended because your new main breaker will allow up to 100 amps and your old wire can only safely handle 60amps. If you put a 60amp main breaker in the new box, that would be acceptable. No, it is perfectly safe. Because the box is overrated, there is no problem. If the box is the main panel, and not a subpanel, install a 60A main breaker so you cannot overload your service. If it is a subpanel this 60A breaker should be in the main panel.


How do you hook up a 15 amp breaker to a 60 amp box?

If by "60 amp box" you mean a 60-amp service panel (circuit breakers or fuses), you would generally get a 60-A panel that has several slots designed to accept a variety of compatible breakers, from 15A to 60A. If you have a "box" with no breakers, you would need another "subpanel", with wires from the 60A box to the new subpanel, and install one or more 15A breakers in the subpanel. If you don't need more than one breaker, you might also simply use a 15A disconnect panel with a single breaker in it.


Can an apartment charge you for a service dog in training?

Service and assistance animals (or service dogs in training) are not technically pets and owners do not have to pay pet fees. The landlord or apartment, however, can charge a security deposit and may still seek money from the tenant if there is any damage caused by the animal to the home.


What is needed to put a 240V outlet in a garage very close to a circuit panel with NO open slots available?

an electrician. you may have to upgrade your service if not you will need an additional box to accomodate the new breaker Assuming you meet local code and license requirements, and know how to shut things off while you're working: The full circuit panel may be a service panel or a sub-panel with main lugs only (no main disconnect). If it's a sub-panel you need to find the breaker that feeds it from the service panel (if any) to make sure it has enough ampacity to run your 220 appliance on top of whatever is there already. Assuming the breaker and feeder conductors will support the additional load, you can add another subpanel (or replace the existing subpanel with a larger one). If not, you can wire a completely new feeder from the service panel to a new subpanel (or just a 220 disconnect/fuse for your new appliance). If the wiring is old, the minimum disturbance to the existing wiring is recommended: put in a new circuit from the service panel. Some subpanels include extra main lug terminals for feeding other subpanels. Otherwise you can either add another tap to the main lugs and run them to the new subpanel, or else replace two of the existing breakers with a 2-pole breaker that feeds the new subpanel. Put the new 220 circuit into the new panel along with the two old circuits removed from the old full panel to make room for the subfeed breakers.


Country largest Internet provider?

Comcast is the largest cable provider and largest Internet service provider in the United States. When it comes to home phone service, Comcast ranks third on the list.


Which country has the largest postal service?

India


What is the largest sector in the US economy?

service


What is the largest webmail service Is it AOL YAHOO MSN or any other?

In my own opinion, the largest webmail service would be MSN definetely 100%


How did tesla die?

Heart failure. He was found dead on his New Yorker apartment by house service.


Do you need to have telephone service when renting an apartment?

In most cases, phone service is not necessary to rent an aparment. As long as your credit checks out, then you should be eligible.


Is wireless broadband available for free in most apartment complexes?

It depends on the apartment complex you are moving to. Many apartment complex's today offer highspeed internet service or just include it in your rent. The apartments I have stayed in have included it but I know many around me that do not.


Where can a convicted felon find an apartment in Colorado?

In Colorado it's nearly impossible to find any kind of housing for felons. Your best way to find an apartment in Colorado, especially Colorado Springs, is to use an Apartment Locator service, like Apartments Etc. in Colorado Springs. You talk with a 'case manager' and tell them your situation. BE HONEST! They have a list of apartment complexes in your city and they will be able to help you get set up with an apartment that accepts felons. It takes time and energy, but most importantly it takes honesty. If you lie they can not only evict you they can sue you in court. Find an apartment placement service in your city and be honest with them.