answersLogoWhite

0


Best Answer

In the US and Canada, 10 Guage wire will suffice

User Avatar

Wiki User

12y ago
This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: What size wire for 25 amp 110 volt for 75 feet?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

Can you use 60 amp breaker for 110 V at 110 ft and what wire is best?

A breaker is based on wire size, as the breaker protects the wire and not the load. This is a voltage drop question. A #3 copper conductor will limit the voltage drop to 3% or less when supplying 60 amps for 110 feet on a 110 volt system.


Which wire is the neutral wire in a 110 volt system?

White.


What is the minimum ground wire size for a 20 amp 110 volt circuit?

The ground wire in a two or three conductor #12 cable is a #14 bare ground wire.


What size wire for 110 volt 20 amp circuit 250 ft?

A #4 copper conductor will limit the voltage drop to 3% or less when supplying 20 amps for a distance of 250 feet at 120 volts.


What size wire and breaker is needed via 20ft length for a Westonhouse 1500w floodlight?

If it is a 110 volt light it can safely run on a 20 amp circuit with AWG # 12 wire.


What wire size will carry 50 amps 200 ft 110 voltage?

Because of voltage drop, 4 awg copper would be recommended for that distance run. <<>> A #1 copper conductor will limit the voltage drop to 3% or less when supplying 50 amps for 200 feet on a 110 volt system.


What gauge underground wire for 110 volt 15 amp 700 ft for a pond pump?

A #1 copper conductor will limit the voltage drop to 3% when supplying 15 amps for 700 feet on a 120 volt system.


Can you use a neutral wire from a existing 110 volt 20 amp circuit to supply a neutral for a washer dryer combo that has only a 220 volt 30 amp 2 wire?

No !


What size wire do you need to run for 30 amp service to travel trailer 400 feet single phase 110 volt?

Presuming that you would like the least expensive installation, the following is calculated on overhead aluminum wire. The wire size needed to hold the voltage drop to 3% would be 3/0 MCM. If the installation could be run on 240 volts then the wire size can be reduced to #2.


How many square feet are in 110 x 110 size room?

110 feet x 110 feet = 12,100 square feet (this, incidentally, is a very large room).


How do you wire 220 volt from 2 110 volt lines. you have a concessions stand that is wired for 220 but everywhere you have been lately just keeps giving you 2 - 110 volt line?

If you combine two 110 volt power lines it does not give you 220 volts, the voltage will be the same. The only way to turn 110 volts into 220 volts is with a step-up transformer.


What size of earth wire can be used in wiring system?

You will need to look up cabling/wiring codes.Is it:Telephony,Audio distribution,110 volt power lines, orHigher voltage power lines?