answersLogoWhite

0

A voltage needs to be stated. Assuming the question is from North America 120 volts will be used. Assuming that the 800 watts is for each outlet that is a total of 2400 watts. The electrical code states that a conductor in continuous use can only be loaded to 80% capacity. I = W/E = 2400/120 = 20 amps. A #14 conductor is rated at 15 amps x 80% = 12 amps. A #10 conductor is rated at 30 amps x 80% = 24 amps.

So to answer the question, no a 14 gauge wire and a 15 amp breaker will not handle 3 outlets using 800 watts.

User Avatar

Wiki User

12y ago

What else can I help you with?

Related Questions

Should you use 14-2 or 12-2 for garage outlets and lights in Richfield mn?

The only determining factor is the size of the circuit breaker that you will be using. If the garage circuit will be protected with a 15 Amp breaker, you may use a 14 AWG wire. If the circuit will be protected with a 20 amp breaker, you must use a 12 AWG wire. Note too that garage outlets should be protected with a GFCI breaker or outlet. If you have any concerns regarding your ability to adequately design and install the garage outlets, please, for your own safety, contact a local electrician.


Can you put 20amp breaker on 10-2 wire?

No, you should match the breaker size to the wire gauge. A 10-2 wire is typically rated for a 30 amp breaker. Using a 20 amp breaker on 10-2 wire could result in overheating and a potential fire hazard.


How can I safely create a daisy chain of electrical outlets in my home?

To safely create a daisy chain of electrical outlets in your home, you should first ensure that the circuit can handle the additional load. Use proper wiring techniques, such as connecting outlets in series and using appropriate wire gauge. It is recommended to consult a licensed electrician to ensure the work is done safely and up to code.


What size circuit breaker for GFCI circuit in a normal size bath?

Normally it is a 20 amp using AWG 12/2 gauge wire. But it really depends on what size wire is on that circuit. If it is white AWG 14 gauge then use a 15 amp breaker. If it is yellow AWG 12 gauge then use a 20 amp breaker.


How can I securely fasten a breaker handle to a tie?

You can securely fasten a breaker handle to a tie by using a zip tie or a small piece of wire to tightly wrap around the handle and the tie. Make sure it is snug and secure to prevent any movement.


Can you connect 14 gauge wire to 12 gauge wire on a 20 amp breaker if the 14 gauge is the end of the run and dedicated to lights?

yesAnother (corrected) answer.NO! The circuit breaker is there to protect the wiring from overheating. It wouldn't matter where on the circuit you decided to put the 14 gauge wire, you would need to change the breaker to 15 Amp if you did that. Using 14 gauge wire on a 20 amp circuit is a fire hazard and contrary to UBC. Contact your local building and zoning department to verify.


How much can a 15W circuit breaker handle?

Answer for the US: Breakers are rated in amps, not watts. However, a 15A breaker can handle 15 amps, or about 1800 watts (using 120V), or 3600 watts (using 240V). However, this is only rated for noncontinuous loads (those not lasting for more than three hours). For continuous loads (loads lasting three hours or more), one must derate the circuit breaker by 80%. So for continuous loads, that same breaker should only have 1440 watts (using 120V), or 2880 watts (using 240V) on it.


Is a 12 gauge wire on 20 amp breaker safe for a sub panel?

No, a 12 gauge wire is rated for 20 amps, which matches the breaker size. It is not recommended to use a wire that matches the breaker size as it can result in overheating and potentially cause a fire hazard. Consider using a thicker wire, such as 10 gauge, for the 20 amp breaker to ensure safety for the sub panel.


Is connecting 20 amp breaker to 14 gauge wire safe?

No, connecting a 20 amp breaker to 14 gauge wire is not safe. The National Electrical Code (NEC) specifies that 14 gauge wire is rated for a maximum of 15 amps. Using a 20 amp breaker could lead to overheating and potentially cause a fire hazard if the wire is overloaded. It is recommended to use 12 gauge wire for a 20 amp circuit to ensure safety and compliance with electrical codes.


How many 20amp outlets in commercial building per circuit?

All depends on how big your main breaker is and what size wire you are using,one 20 amp outlet needs #12 wire not more than 50feet away from main breaker


What size wire to run 100' from panel using a 30amp breaker for a RV?

For a 100' run from the panel to the RV using a 30amp breaker, you should use 10 gauge wire to ensure safe and efficient power delivery. This wire gauge is appropriate for the distance and the current capacity of the breaker.


How many plugs with 15 amp 14 gauge wire?

It depends on the load. In a normal home I would not install more than a combination of 12 outlets and lights on a 15 amp circuit. But if the room is an office room with lots of electronics then I would limit it to a combination of 10.