answersLogoWhite

0


Best Answer

It will taken 8 amps

<<>>

The conversion of 2.5 sq mm wire to AWG is equal to a #12 wire. The ampacity of a #12 copper wire with an insulation factor of 90 degrees C is 20 amps.

User Avatar

Wiki User

12y ago
This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: How many amps can a 2.5 sq mm wire conduct?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Continue Learning about Electrical Engineering

How many amps can a 8 gauge wire run coming from the ditribution panel to the sub panel 25 feet away?

A #8 copper wire with an insulation factor of 75 or 90 degrees C is rated at 45 amps.


Can you run a 2 kw convector heater through a 25 amp trip switch at 240 volts?

Yes, the total amperage load of a 2000 watt heater at 240 volts is 8.3 amps. Keep in mind that the wire feeding the heater must be a #10 because the breaker is rated at 25 amps. A wire's ampacity rating can be larger that the breaker amperage rating but never smaller. Example, a #14 rated at 15 amps or a #12 rated at 20 amps can not be connected to a 25 amp breaker. The 25 amp breaker does not trip until it reaches 25 amps well over the allowable amperage of the #14 amd #12 wire. This is why a #10 wire must be used as its rating is 30 amps.


Should 25 amps breaker be replaced by 20 amps?

For typical residential house wiring 12 AWG wire is required for a 20 Amp breaker. If you change out the breaker for a 25 A breaker you would have to rewire the circuit with 10 AWG. In that case you could up the breaker to 30 Amps. All outlets and switches should be rated at the same voltage and current as the breaker.


Can you use 10 AWG wire to run 6000 watts of light drawing 30 amps?

I'm assuming the electrical system is single phase, such as a home. If not, you need to hire someone to do the work for you. First, 6000 watts at 120v is 50 amps, so if your load is truly 6000 watts, 30 amps isn't enough. If your 6000 watts is 240v, which would draw 25 amps, then 30 amps is plenty. Ten gauge wire may not be placed an a breaker or fuse larger than 30 amps.


How do you replace a 15 amp circuit to a 25 amp circuit?

You have to rewire the circuit completely with 10 AWG wire and replace all outlets and switches with devices rated at 25 Amps. Note 25 Amp breaker is an unusual size. 10 AWG will go up to 30 amps, and that would be the way to go.

Related questions

How many amps can a 8 gauge wire run coming from the ditribution panel to the sub panel 25 feet away?

A #8 copper wire with an insulation factor of 75 or 90 degrees C is rated at 45 amps.


How many amps can 16 gauge wire carry at 120 vac at 25 feet?

A 16 gauge wire can typically carry around 10-13 amps at 120V AC over a short distance like 25 feet. It's important to follow standard safety practices and consult with an electrician to ensure that the wire gauge is appropriate for your specific application and local electrical code requirements.


How many amps can 8 gauge wire carry at 120 vac at 25 feet?

8 gauge wire can typically carry up to 40 amps at 120 volts AC over a distance of 25 feet. However, it is important to consult the specific wire manufacturer's specifications and consider other factors such as temperature, installation conditions, and local electrical codes when determining the ampacity of the wire for a particular application.


Can you run a 2 kw convector heater through a 25 amp trip switch at 240 volts?

Yes, the total amperage load of a 2000 watt heater at 240 volts is 8.3 amps. Keep in mind that the wire feeding the heater must be a #10 because the breaker is rated at 25 amps. A wire's ampacity rating can be larger that the breaker amperage rating but never smaller. Example, a #14 rated at 15 amps or a #12 rated at 20 amps can not be connected to a 25 amp breaker. The 25 amp breaker does not trip until it reaches 25 amps well over the allowable amperage of the #14 amd #12 wire. This is why a #10 wire must be used as its rating is 30 amps.


What size wire to carry 25 amps 170 ft?

To answer this question a voltage must be given.


What size wire needed for 25 amps 220 volts for 75 feet?

For a 25 amp load at 220 volts over a distance of 75 feet, you will need a 10-gauge wire to ensure safe and efficient electrical conductivity. This wire size allows for minimal voltage drop and meets the necessary ampacity requirements for the circuit. Make sure to consult local electrical codes and regulations before installation.


How many automotive amps can 30 foot strand of copper wire carry?

The number of automotive amps a 30-foot strand of copper wire can carry depends on the gauge (thickness) of the wire. For example, a 30-foot strand of 10-gauge copper wire can typically carry up to 40-50 amps for automotive use, while a 30-foot strand of 12-gauge wire might be limited to around 25-30 amps. It's important to consult wire ampacity tables and consider factors like temperature and voltage drop to ensure safe and effective performance.


How many amps in 25 ma?

.025amps


What gauge wire is required for 25 amps over 100 ft at 240 volts?

10 AWG copper.


How many amps in a 4mm wire?

The current-carrying capacity of a wire depends on various factors, such as material and insulation. However, a general guideline is that a 4mm wire can typically carry around 25-30 amps of current. It is important to consult specific standards or regulations for precise information.


What is amperage limit of 12 AWG stranded copper wire?

For 12 AWG stranded copper wire, the amperage limit is typically around 25 to 30 amps for general power transmission applications. However, this can vary based on factors such as the insulation type, installation environment, and specific regulations or standards that apply. It is always recommended to consult a qualified electrician or reference the appropriate codes and standards for your specific application.


Can a 14 AWG solid copper wire that's 15 feet long carry a load of 40 amps?

No, a #14 conductor is only rated for 15 amps. If the wire insulation is rated for 90 degrees C and is connected to a 90 degree rated circuit breaker the ampacity can be raised to 25 amps.