Normally it is a 20 amp using AWG 12/2 gauge wire. But it really depends on what size wire is on that circuit. If it is white AWG 14 gauge then use a 15 amp breaker. If it is yellow AWG 12 gauge then use a 20 amp breaker.
For a 100 Amp breaker panel it would be 2 AWG. For 150 Amps it would require 2/0 (2 ought) aluminum wire.
You listed no gauge wire. This is the required breakers.14 gauge - 15 amp12 gauge - 20 amp10 gauge - 30 amp8 gauge - 40 amp
14 gauge will handle it with a 15 amp breaker. If you use 12 gauge use a 20 amp breaker.
In standard construction this would require a 15 amp breaker and 14 gauge copper wire.
Copper wire gauge sizes are not equivalent to aluminum wire gauge sizes. The gauge sizes for copper and aluminum wires are different due to their differing electrical conductivity properties. It is not possible to directly convert a copper wire size to an equivalent aluminum wire size.
A 14 gauge wire is typically used on a 15 amp circuit breaker. It is not recommended to use a larger circuit breaker with a smaller wire size as this can create a fire hazard.
Don't use aluminum wire inside the house.
Normally it is a 20 amp using AWG 12/2 gauge wire. But it really depends on what size wire is on that circuit. If it is white AWG 14 gauge then use a 15 amp breaker. If it is yellow AWG 12 gauge then use a 20 amp breaker.
30 amp breaker with #10 gauge copper wire
For a 100 Amp breaker panel it would be 2 AWG. For 150 Amps it would require 2/0 (2 ought) aluminum wire.
You listed no gauge wire. This is the required breakers.14 gauge - 15 amp12 gauge - 20 amp10 gauge - 30 amp8 gauge - 40 amp
Wire size is rated by Amperes of current. You did not mention the wire size of the aluminum wire, so there is no way to answer your question. The voltage rating is more a rating of how good the insulation around the wire is.
14 gauge will handle it with a 15 amp breaker. If you use 12 gauge use a 20 amp breaker.
You can use a 20-amp single pole breaker for 12-2 wire. This is the standard size breaker for 12-gauge wire in residential applications.
The size of the main breaker depends on the maximum current rating of the 10 gauge wire and the load it will be powering. Typically, a 10 gauge wire is rated for a maximum current of 30 amps. Therefore, a 30 amp main breaker would be suitable for running 10 gauge wire. However, it is important to consult local electrical codes and consider the specific load requirements before making a final determination.
For 6 gauge wire, typically you would use a 60 amp breaker for larger appliances like a dryer or cooktop. However, always consult with a licensed electrician to ensure the proper breaker size for your specific application and local electrical code requirements.