answersLogoWhite

0

That distance you are going to have to install a sub-panel and run AWG # 4 wire and even then you will have a voltage drop of 7.45 volts giving you 232.55 volts at the sub-panel which is acceptable.

User Avatar

Wiki User

11y ago

What else can I help you with?

Continue Learning about Electrical Engineering

What size breaker do you need for 5.7kw neff oven?

A breaker is sized by the wire size. The wire is sized by the amperage. The formula for amperage is I = W/E. Amps = Watts/Volts. As you can see with no voltage stated an answer can not be given.


What size breaker do you need for two 60W bulbes 110 volts?

It is not the number of bulbs that you worry about. It is the wire size that is your concern. If the circuit is wired with AWG 12/2 wire then use a 20 amp breaker. If it is wired with a AWG 14/2 wire then use a 15 amp breaker. You are protecting the wiring with the correct size breaker.


What size amp circuit breaker would protect a 12kW boiler?

The breaker protects the wiring not the boiler. 12,000 watts at 240 volts will require 50 amps. So, you will need a 60 amp breaker using AWG# 6 wire on a dedicated circuit.


Can you use 40 amp breaker for your lights and plug ins?

If you are referring to house wiring then the answer is no. A breaker protects the wire size that is connected to the breaker. In home wiring most homes are wired with a #14 wire which is rated at 15 amps. That is why the wire is protected by a 15 amp breaker. The correct wire size to connect to a 40 amp breaker is a #8. This size wire is too large to connect to receptacles an light fixture terminals.


How do you connect wire to a breaker?

There is 220 volts between the two poles. If you are running 2 wires (black and white) + ground then you hook black to one pole and white to the other. Put red or black electric tape on each end of the white wire and wrap around wire for 3 inches or so next to the connection so the next person will be able to see that the wire is hot and not a neutral.

Related Questions

What size breaker do you need for 5.7kw neff oven?

A breaker is sized by the wire size. The wire is sized by the amperage. The formula for amperage is I = W/E. Amps = Watts/Volts. As you can see with no voltage stated an answer can not be given.


What size breaker do you need for two 60W bulbes 110 volts?

It is not the number of bulbs that you worry about. It is the wire size that is your concern. If the circuit is wired with AWG 12/2 wire then use a 20 amp breaker. If it is wired with a AWG 14/2 wire then use a 15 amp breaker. You are protecting the wiring with the correct size breaker.


How do you wire a wire to a wire?

If you are connecting 120 volts, you connect the black wire to the breaker, white wire to the neutral bar, and ground wire to the ground bar. If you are connecting 240 volts connect the black & white wires to the breaker, & ground wire to the ground bar.


What size amp breaker you need for a ac and a heater unit?

The sizing of a breaker is dependant upon the size of the wire it protects. The size of the wire is dependant upon what the load current in amps is. Without the amperage and wattage and the voltage of the appliances an answer can not be given. W = A x V, Amps = Watts/ Volts.


What is the recommended wire size for a 50amp breaker?

The recommended wire size for a 50 amp breaker is typically 6-gauge wire.


When installing a circuit breaker do you size the breaker to correct wire size or the device its controlling?

When installing a circuit breaker, you size the breaker based on the wire size. The breaker should be matched to the ampacity of the wire to ensure proper protection against overloads and short circuits. The device being controlled by the breaker is not a determining factor in sizing the breaker.


What is the recommended wire size for a 20 amp breaker?

The recommended wire size for a 20 amp breaker is typically 12-gauge wire.


What is the appropriate wire size for a 25 amp breaker?

The appropriate wire size for a 25 amp breaker is typically 10 gauge wire.


What is the appropriate wire size for a 30 amp breaker?

The appropriate wire size for a 30 amp breaker is typically 10 gauge wire.


What is the recommended wire size for a 25 amp breaker?

The recommended wire size for a 25 amp breaker is typically 10 gauge wire.


What is the recommended wire size for a 30 amp breaker?

The recommended wire size for a 30 amp breaker is typically 10 gauge wire.


What is the recommended wire size for a 50 amp breaker?

The recommended wire size for a 50 amp breaker is typically 6-gauge wire.