No. 20 amps at 120 volts will handle a maximum of 2400 watts. And you should never continuously load a 20 amp 120 volt circuit to no more than 1920 watts.
Chat with our AI personalities
Answer for USA, Canada and countries running a 60 Hz power supply service. Watts= voltage X amps At 120 volt total watts would be 2400 at 20 amps. The electrical code states that circuit conductors that are fed by this breaker on a continuous load can only be loaded to 80%. #12 wire rated at 20 amps, derated to 16 amps continuous = 16 x 120 = 1920 watts, #10 wire rated at 30 amps derated to 24 amps continuous = 24 x 120 = 2880 watts. On load calculations this derate should be taken into consideration. To maintain the required wattage needed for the load the wire size and/or the next size breaker may be needed.
A #12 wire can carry 20 amps. Assuming the connected voltage is 120 volts the wattage will be Watts = Amps x Volts. W = 20 x 120 = 2400 watts. The circuit can legally be loaded to 80%. 2400 x 80% = 1920 watts. The maximum amount of loads that can be connected to a 20 amp #12 wire have to be added up individually but stay under 1920 watts.
To determine the appropriate amp breaker for a 3700-watt element, you can use the formula: Amps = Watts / Volts. Assuming a standard voltage of 240 volts, the calculation would be 3700 watts / 240 volts = approximately 15.4 amps. It is advisable to use a 20-amp breaker for safety and to accommodate any inrush current, ensuring the breaker can handle the load without tripping.
Yes but you will not get the full watt rating out of the tank. Watts = amps x volts. Say the tank draws 20 amps. 20A x 240V = 4800 watts. 20A x 208V = 4160 watts. It will take longer to heat your water with less wattage.
To answer this question the voltage has to be given. I = W/E. Amps = Watts/Voltage.