No. You need 20 amp receptacles. ( if a single receptacle on an individual brach circuit NEC 210.21 (B)(1) )

Yes you can use a 15 amp receptacles on a 20 amp breaker in the states but not in Canada. ( branch circuit supplying two or more receptacle NEC 210.21(B)(3) )

15 amp receptacle on a 20 amp circuit is not code, partly because 20 amp circuits use #10 ga wire, which does not fit unto a 15 amp receptacle,(can be forced but lots of work.) Also a 15 amp receptacle will not take the 18 amps continuios that a 20 amp recep. will. ( It is code, see above. 14 awg = 15 amp, 12 awg = 20 amp, 10 awg = 30 amp )

20 amp wire is 12 gauge not 10

Yes you can use 15A outlets and swithes on 20 amp breakers they are UL listed for 20 amp even if they are stamped for 15A as long as the wire is 12ga to. ( NEC Table 210.21 (B)(3) )

User Avatar

Wiki User

9y ago

What else can I help you with?

Related Questions

How many outlets can be safely connected to a 30 amp circuit?

A 30 amp circuit can safely support up to 4 outlets.


How many 15 amp outlets can be safely installed on a 20 amp circuit?

On a 20 amp circuit, it is safe to install up to 13 outlets that are rated for 15 amps each.


How many elec outlets can a GFCI detect?

A GFCI can detect ground faults on the specific circuit it is connected to. If multiple outlets are on the same circuit protected by a single GFCI outlet, the GFCI can protect all of them. However, if the outlets are on different circuits or not downstream from the GFCI, they would need their own GFCI protection.


What size circuit breaker do you need for kichen counter outlets?

Two 20 Amp circuits with the outlets staggered so a different circuit is on two adjacent outlets. Should be GFCI protected.


Can amp meters be connected in series and both read the same?

When connected in series, multiple amp meters in the same circuit should read the same.


How many outlets are there?

Up to 12 on a 20 amp circuit. Up to 9 on a 15 amp circuit. But use common sense. If the circuit will be heavily loaded, as in a home office, then do not install that many.


Is it possible to operate two 1300 W hairdryers on a 120 V circuit without blowing a fuse?

1300 watts on a 120 volt circuit is 10.8 amps. Since most circuits are built with 15 or 20 amp breakers, no. Rdrsh is correct. If both outlets you plan on using are on the same circuit and you have nothing else on, you might be able to run both at the same time for a short period of time if it is a 20 amp circuit. If it is a 15 amp circuit, no way will it work. However if you have a couple of 100 watt lights on then you will have a total of over 20 amps draw and it will trip the breaker. You need to have these of separate circuits.


How many lighting outlets are permitted on a branch circuit?

The National Electrical Code typically allows a maximum of 12 lighting outlets on a 15-amp branch circuit and 16 lighting outlets on a 20-amp branch circuit. However, these numbers can vary based on local code requirements, so it's important to check with your local authority having jurisdiction.


Can you use a 15 amp 110 outlet on a 20 amp circuit as I am replacing my old outlets with new duplex ones and realized that three of my Kitchen outlets are on one 20 amp breaker?

Yes, you can use a 15 amp outlet on a 20 amp circuit. The outlets are designed to be compatible with different amperages. Just ensure that the wiring is correctly sized for a 20 amp circuit to avoid any safety issues.


Can the power to your whirlpool be on the same 20 amp circuit as the bathroom lights and outlets?

No, the whirlpool has a motor load connected to it and should be connected to a dedicated ground fault breaker.


How many outlets can run off 1 gfi outlet?

Eight on a 15 amp circuit, tweleve on a 20 amp circuit, including the gfci receptacle itself.


How many computer outlets can go on a 10 amp circuit?

About 8 amps worth, if you derate the circuit for 100 percent duty cycle.