No. You need 20 amp receptacles. ( if a single receptacle on an individual brach circuit NEC 210.21 (B)(1) )

Yes you can use a 15 amp receptacles on a 20 amp breaker in the states but not in Canada. ( branch circuit supplying two or more receptacle NEC 210.21(B)(3) )

15 amp receptacle on a 20 amp circuit is not code, partly because 20 amp circuits use #10 ga wire, which does not fit unto a 15 amp receptacle,(can be forced but lots of work.) Also a 15 amp receptacle will not take the 18 amps continuios that a 20 amp recep. will. ( It is code, see above. 14 awg = 15 amp, 12 awg = 20 amp, 10 awg = 30 amp )

20 amp wire is 12 gauge not 10

Yes you can use 15A outlets and swithes on 20 amp breakers they are UL listed for 20 amp even if they are stamped for 15A as long as the wire is 12ga to. ( NEC Table 210.21 (B)(3) )

User Avatar

Wiki User

9y ago
This answer is:
User Avatar
More answers
User Avatar

AnswerBot

6mo ago

It is generally not recommended to mix 15 amp and 20 amp outlets on the same circuit because it can create a safety hazard. If the circuit is protected by a 15 amp breaker, using a 20 amp outlet could lead to overheating and potentially cause a fire. It's best to match the outlet amperage with the circuit breaker amperage for safety and code compliance.

This answer is:
User Avatar

User Avatar

Wiki User

15y ago

In Canada there shall be not more that 12 outlets on any 2 wire branch circuit. Such outlets shall be considered to be rated at not more that 1 amp per outlet. Where the connected load is known, the number of outlets may exceed 12 providing the load current does not exceed 80 % of the rating of the over current device protecting the circuit.

This answer is:
User Avatar

User Avatar

Wiki User

9y ago

In the United States this is acceptable provided it is at least a duplex receptacle or it is not the only receptacle on the circuit. A 15A receptacle will only allow devices rated at 15A or less to be plugged into them.

This answer is:
User Avatar

User Avatar

Wiki User

14y ago

Not a good idea. Match the devices to the rating of the breaker protecting the circuit.

This answer is:
User Avatar

User Avatar

Wiki User

14y ago

Yes. A higher rating is allowed.

This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: Can you use both 15 amp and 20 outlets on the same circuit?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

How many elec outlets can a GFCI detect?

A GFCI can detect ground faults on the specific circuit it is connected to. If multiple outlets are on the same circuit protected by a single GFCI outlet, the GFCI can protect all of them. However, if the outlets are on different circuits or not downstream from the GFCI, they would need their own GFCI protection.


What size circuit breaker do you need for kichen counter outlets?

Two 20 Amp circuits with the outlets staggered so a different circuit is on two adjacent outlets. Should be GFCI protected.


Can amp meters be connected in series and both read the same?

When connected in series, multiple amp meters in the same circuit should read the same.


How many outlets are there?

Up to 12 on a 20 amp circuit. Up to 9 on a 15 amp circuit. But use common sense. If the circuit will be heavily loaded, as in a home office, then do not install that many.


How many lighting outlets are permitted on a branch circuit?

The National Electrical Code typically allows a maximum of 12 lighting outlets on a 15-amp branch circuit and 16 lighting outlets on a 20-amp branch circuit. However, these numbers can vary based on local code requirements, so it's important to check with your local authority having jurisdiction.


Is it possible to operate two 1300 W hairdryers on a 120 V circuit without blowing a fuse?

1300 watts on a 120 volt circuit is 10.8 amps. Since most circuits are built with 15 or 20 amp breakers, no. Rdrsh is correct. If both outlets you plan on using are on the same circuit and you have nothing else on, you might be able to run both at the same time for a short period of time if it is a 20 amp circuit. If it is a 15 amp circuit, no way will it work. However if you have a couple of 100 watt lights on then you will have a total of over 20 amps draw and it will trip the breaker. You need to have these of separate circuits.


Can you use a 15 amp 110 outlet on a 20 amp circuit as I am replacing my old outlets with new duplex ones and realized that three of my Kitchen outlets are on one 20 amp breaker?

Yes, you can use a 15 amp outlet on a 20 amp circuit. The outlets are designed to be compatible with different amperages. Just ensure that the wiring is correctly sized for a 20 amp circuit to avoid any safety issues.


How many outlets can run off 1 gfi outlet?

Eight on a 15 amp circuit, tweleve on a 20 amp circuit, including the gfci receptacle itself.


Can the power to your whirlpool be on the same 20 amp circuit as the bathroom lights and outlets?

No, the whirlpool has a motor load connected to it and should be connected to a dedicated ground fault breaker.


How many outlets are allowed on a 240 v branch circuit?

Branch circuit loading In Canada the CEC states that there shall be not more than 12 outlets on any 2-wire branch circuit. These outlets shall be considered to be rated at not less than 1 amp per outlet Where the connected load is known, the number of outlets shall be permitted to exceed 12, provided that the load current does not exceed 80% of the rating of the over current device protecting the circuit. For example on a 15 amp breaker, 15 x 80% = 12 amps, hence the standard of 12 outlets on any 2-wire branch circuit. On a 20 amp breaker, 20 x 80% = 16 amps. So from a 20 amp breaker this allows 16 outlets on a 2-wire branch circuit as long as the outlets are not considered to be rated at less than 1 amp per outlet. The definition of an outlet is a point in the wiring installation at which current is taken to supply utilization equipment. What this means is that if a light switch and a fixture outlet were on the same 2-wire branch circuit they would be subtracted from the maximum count of 12 receptacle outlets on the circuit which would leave 10. If the light fixture draws 3 amps plus the switch outlet, then the total circuit outlet count would be reduced to 8 receptacle outlets (12 -- 3 -- 1 = 8). On a standard specification home most electricians will wire one circuit per room, the outlet count usually never reaches the maximum of 12 outlets.


How many computer outlets can go on a 10 amp circuit?

About 8 amps worth, if you derate the circuit for 100 percent duty cycle.


How many wall outlets can you have in a circuit using a A breaker?

Assuming this is not an office of a place where lots of the outlets will be used to power items that draw lots of current on a 15 amp circuit wired with 14/2 wire I would limit it to no more than 10 outlets and lights combined. On a 20 amp circuit wired with 12/2 wire I would limit it to a 14 outlets and lights combined. There is no limit in the code. You just use common sense based on what is going to be used on this circuit.