You can use 90 degree celcius rated wire. It just must be derated to the 75 degree column in the book NFPA 70 article 310.16 table. Meaning, if you are running romex wire, you don't have to run larger wire in most situations.

User Avatar

Wiki User

βˆ™ 14y ago
This answer is:
User Avatar
More answers
User Avatar

AnswerBot

βˆ™ 5mo ago

It is not recommended to use 90-degree wire with a breaker that specifies 75-degree wire unless it is specifically allowed by the manufacturer or electrical code. Using a wire with a lower temperature rating than the breaker can lead to overheating and potential fire hazards. It is important to follow the specified guidelines to ensure safety and proper functioning of the electrical system.

This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: My breaker says use 75 degree wire can i use 90?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

How big of breaker do you use for 115 volt?

Depends on the wire size used in the circuit. If you use AWG # 14 wire you must use a 15 amp breaker. If it is wired with AWG # 12 wire then you use a 20 amp breaker. If a AWG # 10 wire is used then a 30 amp breaker is required. The breaker protects the wiring from overheating so you must use the proper size breaker for the wire used.


What breaker do you use for 10 2 wire?

Use a 30 amp breaker.


What best breaker rating for 1.5 hp air-con unit?

The breaker you use is determined by the size of the wire in the wall not by what is being connected to that circuit. If you have 14/2 wire then use a 15 amp breaker. If you have 12/2 wire then use a 20 amp breaker. The breaker protects the wiring not the item connected.


What best breaker rating for 1.5 hp air con unit?

The breaker you use is determined by the size of the wire in the wall not by what is being connected to that circuit. If you have 14/2 wire then use a 15 amp breaker. If you have 12/2 wire then use a 20 amp breaker. The breaker protects the wiring not the item connected.


Can you use 14-3 wire on a 20amp breaker?

No. A 20 amp breaker needs 12 gauge wire.


Should 25 amps breaker be replaced by 20 amps?

For typical residential house wiring 12 AWG wire is required for a 20 Amp breaker. If you change out the breaker for a 25 A breaker you would have to rewire the circuit with 10 AWG. In that case you could up the breaker to 30 Amps. All outlets and switches should be rated at the same voltage and current as the breaker.


Can you use 10 gauge wire to connect a 2 15 amp outlets to a 30 amp breaker?

No, it is not safe to use 10 gauge wire with a 30 amp breaker as the wire is not rated for that high of a current. It is important to use the correct wire gauge that matches the breaker amperage to prevent overheating and potential fire hazards. For a 30 amp breaker, you should use at least 10 gauge wire.


What size amp circuit breaker should be used for 110 outlet?

The size breaker you use is determined by the size wire used in the circuit. If you use AWG #12/2 wire then use a 20 amp breaker. If you use AWG # 14/2 then use a 15 amp breaker.


What size breaker should you use for a tnia-10 wire?

25 amp breaker


How big of a single pole breaker can you put on 12-2 wire?

You can use a 20-amp single pole breaker for 12-2 wire. This is the standard size breaker for 12-gauge wire in residential applications.


What size wire would you use on a 30amp breaker?

AWG # 10 wire.


Is it safe to use 10 gauge wire on a 20 amp breaker for a microwave?

No, 10 gauge wire requires the use of a 30 amp breaker. A 20 amp breaker is only used on 12 gauge wire.