Depends entirely on current draw. The higher the current, the higher the draw. For example, the wires in a radio may be pretty small, while the wire to operate your stove is pretty large. The wires to operate an overhead electric locomotive or trolley may be 8 to 12 inches across.

In house wiring, the standard in most places is 14 guage for the lighting circuits, 12 guage for the convenience outlets, and bigger guages for the clothes dryer and stove.

User Avatar

Wiki User

14y ago
This answer is:
User Avatar
More answers
User Avatar

AnswerBot

5mo ago

The size of wire needed for an AC unit depends on the ampacity of the unit. It is recommended to consult the manufacturer's specifications or a qualified electrician to determine the appropriate wire size. Typically, a 12-gauge wire is used for 20-amp circuits and a 10-gauge wire for 30-amp circuits.

This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: What size wire do you need for AC?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

What is the wire size for a 35 amp breaker to a ac unit?

You will need to use #8 wire.


What size wire do i need for a 16500 btu marine ac?

Wire size is based on the amperage of the connected load. Without that amperage an answer can not be given.


How do you wire an AC electromagnet?

To wire an AC electromagnet, you would typically connect one end of the coil to the live terminal of the AC power source and the other end to the neutral terminal. It's important to use appropriate wire size and insulation to handle the current and voltage of the AC supply. Additionally, you may need to use a relay or switch to control the circuit.


What size wire do you need to carry nineteen amps for two hundred feet at two hundred forty volts ac?

10 guage


What size wire for 250 v AC?

Wire size is not dependent on voltage - it is dependent on current. Please restate your question and provide the expected branch current.


What is the wire size for 50 amp breaker to ac unit?

For a 50 amp breaker to an AC unit, you would typically use 6-gauge wire. It is important to consult local electrical codes and the manufacturer's specifications for the AC unit to ensure the correct wire size is used for safety and proper operation.


What size amp breaker you need for a ac and a heater unit?

The sizing of a breaker is dependant upon the size of the wire it protects. The size of the wire is dependant upon what the load current in amps is. Without the amperage and wattage and the voltage of the appliances an answer can not be given. W = A x V, Amps = Watts/ Volts.


What size wire do you need to wire a 200 am breaker box?

6


What size wire do you need to connect a camera that's 800' from the power source if it needs 24V AC and it draws 4A and uses 59W?

A gigantic expensive cable run of #8 gauge wire to a 3:1 transformer.


How do you know if the AC breaker matches the AC unit starting demand load?

Read the literature for the ac condensing unit, or the tag on the outside of the unit. Minimum circuit ampacity= minimum breaker, wire and fuse size. Maximum circuit ampacity= the maximum size. Your circuit breaker, wire size and disconnect fuses should all be at or between those 2 numbers.


What size wire do you need for 440 three phase welder on an eight foot run?

The wire size depends on the amperage, not the voltage. The fact that the welder runs on 440 volts does not affect the wire size! You need to ask this question instead: What size wire do you need for a three phase welder on an eight foot run if the nameplate amps are 45A?


What size wire for a 30 amp breaker to ac?