answersLogoWhite

0

A #6 copper wire with an insulation factor of 75 or 90 degree C is rated at 65 amps.

User Avatar

Wiki User

15y ago

What else can I help you with?

Continue Learning about Natural Sciences

What size wire needed for 100 amp service 700 feet away?

A 400 MCM copper conductor will limit the voltage drop to 3% or less when supplying 100 amps for 700 feet on a 240 volt system. This size will allow the conductor to be loaded to 80 amps. 100 x 80% = 80 amps. Conductors are only allowed to be loaded to 80% or their rated capacity. If you need the full 100 amps then you would need to use a wire with a rating of 125 amps. 125 x 80% = 100 amps. A 600 MCM copper conductor will limit the voltage drop to 3% or less when supplying 125 amps for 700 feet on a 240 volt system.


How many amps can 16 gauge wire carry at 120 vac at 25 feet?

A 16 gauge wire can typically carry around 10-13 amps at 120V AC over a short distance like 25 feet. It's important to follow standard safety practices and consult with an electrician to ensure that the wire gauge is appropriate for your specific application and local electrical code requirements.


Exterior electrical service should be 3 feet away from what?

Windows that can be opened.


Exterior electrical service wires should be at least 3 feet away from?

CEC - any window that has the capacity to be opened.The exterior electrical service wires should be at least 3 feet away from any part of any window that is able to be opened.


How many amps can 8 gauge wire carry at 120 vac at 25 feet?

8 gauge wire can typically carry up to 40 amps at 120 volts AC over a distance of 25 feet. However, it is important to consult the specific wire manufacturer's specifications and consider other factors such as temperature, installation conditions, and local electrical codes when determining the ampacity of the wire for a particular application.

Related Questions

How many amps will 2-2-2-4 carry at 180 feet?

150 amps


What size wire will carry 55 amps 75 feet?

AWG # 6 copper


How many amps will 10-2 wire carry at 40 feett?

30 amps is how much a 10-2 wire will carry at 110 feet. 10 gauge wire is only good for thirty amps per the national electrical code. Using 80% of the breakers usage you will actually be getting only 24 amps.


What size wire for 240 volts 200 amp service 200 feet away?

A 3/0 copper conductor will limit the voltage drop to 3% or less when supplying 200 amps for 200 feet on a 240 volt system.


Will awg 10 wire carry 30 amps for 30feet?

Yes, a #10 wire will carry 30 amps for 30 feet. If the load is rated as continuous then the wire will have to be derated to 80% capacity which will leave you with 24 workable amps. If the load demands currents higher that 24 amps then you will have to go to the next wire size up which is a #8 which is rated at 45 amps.


What size wire needed for 100 amp service 700 feet away?

A 400 MCM copper conductor will limit the voltage drop to 3% or less when supplying 100 amps for 700 feet on a 240 volt system. This size will allow the conductor to be loaded to 80 amps. 100 x 80% = 80 amps. Conductors are only allowed to be loaded to 80% or their rated capacity. If you need the full 100 amps then you would need to use a wire with a rating of 125 amps. 125 x 80% = 100 amps. A 600 MCM copper conductor will limit the voltage drop to 3% or less when supplying 125 amps for 700 feet on a 240 volt system.


What wire size is used to make service connection from a 200 amp service panel to a 40 amp service panel 150 feet away?

8 AWG copper is rated for 40 amps. Over 150 ft, at maximum current, the voltage drop would be about 3.76 volts. Using 6 AWG would have a voltage drop of 2.36 volts with the same 40 amps.


What size conductor is needed to carry 25 amps 120 volt AC over 400 feet?

A #4 copper conductor will limit the voltage drop to 3% or less when supplying 25 amps for 400 feet on a 120 volt system.


How many amps can 16 gauge wire carry at 120 vac at 25 feet?

A 16 gauge wire can typically carry around 10-13 amps at 120V AC over a short distance like 25 feet. It's important to follow standard safety practices and consult with an electrician to ensure that the wire gauge is appropriate for your specific application and local electrical code requirements.


How far will 6 gauge wire carry 50 amps?

The distance that a 6 gauge wire can carry 50 amps depends on factors like voltage drop and wire insulation. In general, a 6 gauge wire can carry 50 amps for up to 60-70 feet without significant voltage drop. However, it is recommended to consult with a professional electrician for accurate calculations and safety considerations.


What size wire do you need to carry nineteen amps for two hundred feet at two hundred forty volts ac?

10 guage


What size aluminum wire for 100 amps undergroundservice 60 feet from meter?

A 3/0 aluminum conductor will limit the voltage drop to 3% or less when supplying 150 amps for 150 feet on a 240 volt system. This size will allow the conductor to be loaded to 120 amps. 150 x 80% = 120 Conductors are only allowed to be loaded to 80% or their rated capacity. If you need the full 150 amps then you would need to use a wire with a rating of 190 amps. 190 x 80% = 152 amps A 4/0 aluminum conductor will limit the voltage drop to 3% or less when supplying 190 amps for 150 feet on a 240 volt system.