The breaker will have a black wire connected to it. Turn off the main breaker and then disconnect that black wire from the breaker. The breaker will snap into the main bar. Remove the breaker and install the new one. Reconnect the black wire to the breaker and then install the cover and turn the main breaker back on.
How do you replace a breaker
Answer for USA, Canada and countries running a 60 Hertz supply service.Yes, a 240v 50amp circuit can be changed to a 120v 30amp circuit. The wire for the 50 amp circuit should be a #6. This is more than ample for a 30 amp circuit. Remove the two pole 60 amp breaker and replace it with a single pole 30 and a single pole 15 amp breaker. One of the two #6 wires will be terminated on the neutral bus (if there is a white use it) and the other #6 will be terminated on the new 30 amp breaker. This will give you the required 120 volt 30 amp circuit. The new 15 amp breaker that was installed just to fill the hole from the two pole 60 amp breaker will give you a spare 15 amp circuit. I have no idea what you are trying to do, but there is no way you can change 220v 50 amp to 120v 30 amp. You can take 220 volt input in the top of your circuit breaker box. Then half of one side will be 120v and half of the other side will be 120v. You can install a 30 amp fuse. You should hire an electrician.Before you do any work yourself,on electrical circuits, equipment or appliances,always use a test meter to ensure the circuit is, in fact, de-energizedIF YOU ARE NOT REALLY SURE YOU CAN DO THIS JOBSAFELY AND COMPETENTLYREFER THIS WORK TO QUALIFIED PROFESSIONALS.
No!You cannot simply replace a breaker with a larger one. You would have to tear out ALL of the wiring and replace it with larger. If you just install a larger breaker, you will most likely start a fire, as the existing wiring cannot handle the increased current. You must find the reason the existing breaker is tripping and fix it. If the circuit is overloaded, you will have to either move some of the load to a different circuit, or have the WHOLE circuit upgraded, including wiring and breaker.You will need a licensed electrician to do any repairs or upgrades. You are not qualified to do this work.IF YOU ARE NOT ALREADY SURE YOU CAN DO THIS JOBSAFELY AND COMPETENTLYREFER THIS WORK TO QUALIFIED PROFESSIONALS.If you do this work yourself, always turn off the powerat the breaker box/fuse panel BEFORE you attempt to do any work AND always use a meter or voltage indicatorto insure the circuit is, in fact, de-energized.
Yes. You'll seldom run every circuit to full capacity. The main breaker will trip if all the individual circuits exceed the 200 amp rating of the main breaker.
For an accurate calculation it will be necessary to know what the size of breaker exists in the pump house and what size conductors are used. Power loss is measured using actual amps required, not size of the circuit involved. But the size of circuit (breaker size) can be used. Voltage must also be known.
A circuit breaker will trip if it is faulty or if the connected circuit has a short circuit or a connected device is trying to draw more current than the breaker rating. If you disconnect the output wire from the breaker and it still trips, it is a faulty breaker. If the breaker is tripping immediately when it is turned on then start disconnecting elements of the circuit to see what might be causing the problem. If everything was working and now isn't, it is likely that the wire from the breaker is nicked where it exits the box and is shorting to the feedthru connector.
In the breaker box
in the fuse box ,on the drivers side of the dash.it is a 30 amp circuit breaker.
Answer for USA, Canada and countries running a 60 Hertz supply service.Yes, a 240v 50amp circuit can be changed to a 120v 30amp circuit. The wire for the 50 amp circuit should be a #6. This is more than ample for a 30 amp circuit. Remove the two pole 60 amp breaker and replace it with a single pole 30 and a single pole 15 amp breaker. One of the two #6 wires will be terminated on the neutral bus (if there is a white use it) and the other #6 will be terminated on the new 30 amp breaker. This will give you the required 120 volt 30 amp circuit. The new 15 amp breaker that was installed just to fill the hole from the two pole 60 amp breaker will give you a spare 15 amp circuit. I have no idea what you are trying to do, but there is no way you can change 220v 50 amp to 120v 30 amp. You can take 220 volt input in the top of your circuit breaker box. Then half of one side will be 120v and half of the other side will be 120v. You can install a 30 amp fuse. You should hire an electrician.Before you do any work yourself,on electrical circuits, equipment or appliances,always use a test meter to ensure the circuit is, in fact, de-energizedIF YOU ARE NOT REALLY SURE YOU CAN DO THIS JOBSAFELY AND COMPETENTLYREFER THIS WORK TO QUALIFIED PROFESSIONALS.
Yes, a 30 amp breaker is a 30 amp breaker. It must however be able to fit the box it is installed in.
Sunroof has a 30 amp circuit breaker, position number 26 in the fuse box on the far passenger side of the dash. This circuit breaker also powers the power windows. The circuit breaker can be pulled out and replaced just like a regular fuse.
Yes. You'll seldom run every circuit to full capacity. The main breaker will trip if all the individual circuits exceed the 200 amp rating of the main breaker.
No!You cannot simply replace a breaker with a larger one. You would have to tear out ALL of the wiring and replace it with larger. If you just install a larger breaker, you will most likely start a fire, as the existing wiring cannot handle the increased current. You must find the reason the existing breaker is tripping and fix it. If the circuit is overloaded, you will have to either move some of the load to a different circuit, or have the WHOLE circuit upgraded, including wiring and breaker.You will need a licensed electrician to do any repairs or upgrades. You are not qualified to do this work.IF YOU ARE NOT ALREADY SURE YOU CAN DO THIS JOBSAFELY AND COMPETENTLYREFER THIS WORK TO QUALIFIED PROFESSIONALS.If you do this work yourself, always turn off the powerat the breaker box/fuse panel BEFORE you attempt to do any work AND always use a meter or voltage indicatorto insure the circuit is, in fact, de-energized.
No if the load on the consumer box (circuit breaker panel) were to exceed 60 amps the wire would burn before the fuse blew
For an accurate calculation it will be necessary to know what the size of breaker exists in the pump house and what size conductors are used. Power loss is measured using actual amps required, not size of the circuit involved. But the size of circuit (breaker size) can be used. Voltage must also be known.
it is connected in a box
For a 2002 Ford Explorer, the 30 amp circuit breaker in location #62 of the power distribution box in the engine compartment is the power window circuit breaker. (unfortunately in the 2002 owner's manuals it is labelled accessory delay ) later years are labelled as the power window circuit breaker.
A circuit breaker will trip if it is faulty or if the connected circuit has a short circuit or a connected device is trying to draw more current than the breaker rating. If you disconnect the output wire from the breaker and it still trips, it is a faulty breaker. If the breaker is tripping immediately when it is turned on then start disconnecting elements of the circuit to see what might be causing the problem. If everything was working and now isn't, it is likely that the wire from the breaker is nicked where it exits the box and is shorting to the feedthru connector.