We recommend using a #6 copper wire for the connection between the breaker box and the earth ground rod. This size wire is commonly used for grounding purposes and is sufficient for carrying the electrical current safely to the ground rod. Be sure to consult with a qualified electrician to ensure the proper materials and installation for your specific situation.
For a 1200 amp service, you should use a copper ground wire of at least 3/0 AWG or an aluminum wire of at least 250 kcmil to meet the National Electrical Code requirements. It's always recommended to consult with a licensed electrician to ensure the proper sizing and installation of the ground wire.
A 3/0 copper conductor would allow you up to 100 feet at 800 Amps with only 5 percent voltage drop, assuming 240-volt service. If it were a 3-phase 480-volt service, you could go more than 23 feet with only a 5 percent drop. <<>> The size of conductors for an 800 amp service could be sized in several ways. Using a single conductor is out of the question as the size will be impossible to bend or handle. A 2000MCM wire only has a rating of 775 amps. Most high amperage services will use parallel runs to add up to the required amperage. A parallel run of 600 MCM will give you a total of 910 amps. A triple parallel run of 300 MCM will give you a total of 885 amps. A quad parallel run of 3/0 will give you an amperage of 840 amps. The key here is to find the most economical way of installing the service. Take into account the availability of triple barrel or four barrel lugs, wire costs for the larger sizes and the labour to man handle the larger sizes into the main switch. These size services that I have installed, the customer opted for the four barrel lugs with 3/0 wire. The 3/0 wire is a readily available item even though the lugs may have to be a special order.
For an 800 amp service, typically 4/0 AWG conductors are needed for the hot conductors and 2/0 AWG for the neutral conductor in a 3-phase system. However, it is recommended to consult with a qualified electrician to determine the exact size based on the specific installation requirements and local electrical codes.
For an 800 amp service with parallel sets of 500 kcmil copper conductors, the grounding electrode conductor size should be based on the largest conductor in the parallel set. The grounding electrode conductor size should be sized based on Table 250.66 in the NEC, which recommends a minimum size of 3/0 AWG copper for 1/0 AWG or larger service-entrance conductors.
We recommend using a #6 copper wire for the connection between the breaker box and the earth ground rod. This size wire is commonly used for grounding purposes and is sufficient for carrying the electrical current safely to the ground rod. Be sure to consult with a qualified electrician to ensure the proper materials and installation for your specific situation.
For a 1200 amp service, you should use a copper ground wire of at least 3/0 AWG or an aluminum wire of at least 250 kcmil to meet the National Electrical Code requirements. It's always recommended to consult with a licensed electrician to ensure the proper sizing and installation of the ground wire.
There are two distinct questions here. To determine the wire size to carry 15000 volts the circuits load amperage must be stated. The wire size for a 550 amp service is, an 800 MCM copper conductor with an insulation factor of 90 degrees C. This conductor is rated at 555 amps. Parallel 250 MCM will give you a total capacity of 580 amps. A triple run of 2/0 will give you a total capacity of 585 amps.
A 500 MCM copper conductor will limit the voltage drop to 3% or less when supplying 50 amps for 800 feet on a 120 volt system. 500 MCM wire diameter is 1/2 inch. As you can see there will be trouble getting that size wire into a 50 amp breakers lug. On installations like this to offset the voltage drop at such a low voltage, a transformer should be used at both ends. The first transformer to raise the voltage and the second transformer to lower it at the 800 foot end. If you use two 480 volt transformers a #1 wire can be used between them. A #1 copper conductor will limit the voltage drop to 3% or less when supplying 50 amps for 800 feet on a 480 volt system. By increasing the voltage you can see that a smaller wire size can be used. On an installation of this nature, a primary line should be brought to the RV site and a service distribution panel established at that point and any RV vehicles can then be fed from that service.
Loaded question, what is the voltage, run length, aluminum or copper feeders, expected constant load? Definitely bigger than 4/0
The population of Rea Magnet Wire is 800.
customer service ((800))-923-0024
A 3/0 copper conductor would allow you up to 100 feet at 800 Amps with only 5 percent voltage drop, assuming 240-volt service. If it were a 3-phase 480-volt service, you could go more than 23 feet with only a 5 percent drop. <<>> The size of conductors for an 800 amp service could be sized in several ways. Using a single conductor is out of the question as the size will be impossible to bend or handle. A 2000MCM wire only has a rating of 775 amps. Most high amperage services will use parallel runs to add up to the required amperage. A parallel run of 600 MCM will give you a total of 910 amps. A triple parallel run of 300 MCM will give you a total of 885 amps. A quad parallel run of 3/0 will give you an amperage of 840 amps. The key here is to find the most economical way of installing the service. Take into account the availability of triple barrel or four barrel lugs, wire costs for the larger sizes and the labour to man handle the larger sizes into the main switch. These size services that I have installed, the customer opted for the four barrel lugs with 3/0 wire. The 3/0 wire is a readily available item even though the lugs may have to be a special order.
customer service ((800))-923-0024
A gigantic expensive cable run of #8 gauge wire to a 3:1 transformer.
For an 800 amp service, typically 4/0 AWG conductors are needed for the hot conductors and 2/0 AWG for the neutral conductor in a 3-phase system. However, it is recommended to consult with a qualified electrician to determine the exact size based on the specific installation requirements and local electrical codes.
You will need two 8 foot ground rods. One placed under the meter base and another one placed 6 feet to the side next to the foundation. If this is a home I highly recommend you install a 200 amp service instead of a 100 amp service. Not much more expensive and you will have plenty of room for growth.