Loaded question, what is the voltage, run length, aluminum or copper feeders, expected constant load? Definitely bigger than 4/0

User Avatar

Wiki User

12y ago
This answer is:
User Avatar
More answers
User Avatar

Wiki User

10y ago

#8 bare copper.

This answer is:
User Avatar

User Avatar

Anonymous

Lvl 1
4y ago

480volt length 15’ cooper

This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: What size wire is needed for 800 amp service?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Continue Learning about Electrical Engineering

What size wire needed for 50 amp service 800 feet away 120 volt RV Trailer 3600 watts plus a security light or outdoor outlet What size breaker at the supply disconnect receiving panel disconnect?

A 500 MCM copper conductor will limit the voltage drop to 3% or less when supplying 50 amps for 800 feet on a 120 volt system. 500 MCM wire diameter is 1/2 inch. As you can see there will be trouble getting that size wire into a 50 amp breakers lug. On installations like this to offset the voltage drop at such a low voltage, a transformer should be used at both ends. The first transformer to raise the voltage and the second transformer to lower it at the 800 foot end. If you use two 480 volt transformers a #1 wire can be used between them. A #1 copper conductor will limit the voltage drop to 3% or less when supplying 50 amps for 800 feet on a 480 volt system. By increasing the voltage you can see that a smaller wire size can be used. On an installation of this nature, a primary line should be brought to the RV site and a service distribution panel established at that point and any RV vehicles can then be fed from that service.


What wire size for 15000 Volts and 550 amp service?

There are two distinct questions here. To determine the wire size to carry 15000 volts the circuits load amperage must be stated. The wire size for a 550 amp service is, an 800 MCM copper conductor with an insulation factor of 90 degrees C. This conductor is rated at 555 amps. Parallel 250 MCM will give you a total capacity of 580 amps. A triple run of 2/0 will give you a total capacity of 585 amps.


What is the amperage rating of 800 MCM Copper wire?

600amps


What size wire for a 100 amp service 250 ft run from transformer to home?

This is a voltage drop question. To answer this question a voltage has to be stated. The higher the voltage to the circuit becomes the smaller the wire size needed. After a certain voltage point the wire size will remain constant and the voltage drop at the load will become smaller.


Does a 800 amp service required to be in a one hour rated room?

You obvioulsy do not know what you are talking about. The question as stated makes no sence.

Related questions

What size conductors are needed for 800 amp service?

For an 800 amp service, typically 4/0 AWG conductors are needed for the hot conductors and 2/0 AWG for the neutral conductor in a 3-phase system. However, it is recommended to consult with a qualified electrician to determine the exact size based on the specific installation requirements and local electrical codes.


What size wire is needed for 800 amps?

Loaded question, what is the voltage, run length, aluminum or copper feeders, expected constant load? Definitely bigger than 4/0


What size wire needed for 50 amp service 800 feet away 120 volt RV Trailer 3600 watts plus a security light or outdoor outlet What size breaker at the supply disconnect receiving panel disconnect?

A 500 MCM copper conductor will limit the voltage drop to 3% or less when supplying 50 amps for 800 feet on a 120 volt system. 500 MCM wire diameter is 1/2 inch. As you can see there will be trouble getting that size wire into a 50 amp breakers lug. On installations like this to offset the voltage drop at such a low voltage, a transformer should be used at both ends. The first transformer to raise the voltage and the second transformer to lower it at the 800 foot end. If you use two 480 volt transformers a #1 wire can be used between them. A #1 copper conductor will limit the voltage drop to 3% or less when supplying 50 amps for 800 feet on a 480 volt system. By increasing the voltage you can see that a smaller wire size can be used. On an installation of this nature, a primary line should be brought to the RV site and a service distribution panel established at that point and any RV vehicles can then be fed from that service.


What wire size to use from breaker box to earth ground rod?

We recommend using a #6 copper wire for the connection between the breaker box and the earth ground rod. This size wire is commonly used for grounding purposes and is sufficient for carrying the electrical current safely to the ground rod. Be sure to consult with a qualified electrician to ensure the proper materials and installation for your specific situation.


What wire size for 15000 Volts and 550 amp service?

There are two distinct questions here. To determine the wire size to carry 15000 volts the circuits load amperage must be stated. The wire size for a 550 amp service is, an 800 MCM copper conductor with an insulation factor of 90 degrees C. This conductor is rated at 555 amps. Parallel 250 MCM will give you a total capacity of 580 amps. A triple run of 2/0 will give you a total capacity of 585 amps.


What size ground wire should you use on a 1200 amp service?

For a 1200 amp service, you should use a copper ground wire of at least 3/0 AWG or an aluminum wire of at least 250 kcmil to meet the National Electrical Code requirements. It's always recommended to consult with a licensed electrician to ensure the proper sizing and installation of the ground wire.


What is Rea Magnet Wire's population?

The population of Rea Magnet Wire is 800.


Gmail customer service ((800))-923-0024 service talk to person is correct number?

customer service ((800))-923-0024


What size ungrounded conductor for 800 amp service?

A 3/0 copper conductor would allow you up to 100 feet at 800 Amps with only 5 percent voltage drop, assuming 240-volt service. If it were a 3-phase 480-volt service, you could go more than 23 feet with only a 5 percent drop. <<>> The size of conductors for an 800 amp service could be sized in several ways. Using a single conductor is out of the question as the size will be impossible to bend or handle. A 2000MCM wire only has a rating of 775 amps. Most high amperage services will use parallel runs to add up to the required amperage. A parallel run of 600 MCM will give you a total of 910 amps. A triple parallel run of 300 MCM will give you a total of 885 amps. A quad parallel run of 3/0 will give you an amperage of 840 amps. The key here is to find the most economical way of installing the service. Take into account the availability of triple barrel or four barrel lugs, wire costs for the larger sizes and the labour to man handle the larger sizes into the main switch. These size services that I have installed, the customer opted for the four barrel lugs with 3/0 wire. The 3/0 wire is a readily available item even though the lugs may have to be a special order.


AOL customer service number ((800))-923-0024 service talk to person is correct number?

customer service ((800))-923-0024


What size wire do you need to connect a camera that's 800' from the power source if it needs 24V AC and it draws 4A and uses 59W?

A gigantic expensive cable run of #8 gauge wire to a 3:1 transformer.


What is the customer service phone number for Qwest?

Qwest have several customer service phone numbers. The list are customer service: 1-800-201-4099. Business customer service: 1-800-201-4102. Internet customer service: 1-800-788-3600