Loaded question, what is the voltage, run length, aluminum or copper feeders, expected constant load? Definitely bigger than 4/0
Chat with our AI personalities
A 500 MCM copper conductor will limit the voltage drop to 3% or less when supplying 50 amps for 800 feet on a 120 volt system. 500 MCM wire diameter is 1/2 inch. As you can see there will be trouble getting that size wire into a 50 amp breakers lug. On installations like this to offset the voltage drop at such a low voltage, a transformer should be used at both ends. The first transformer to raise the voltage and the second transformer to lower it at the 800 foot end. If you use two 480 volt transformers a #1 wire can be used between them. A #1 copper conductor will limit the voltage drop to 3% or less when supplying 50 amps for 800 feet on a 480 volt system. By increasing the voltage you can see that a smaller wire size can be used. On an installation of this nature, a primary line should be brought to the RV site and a service distribution panel established at that point and any RV vehicles can then be fed from that service.
There are two distinct questions here. To determine the wire size to carry 15000 volts the circuits load amperage must be stated. The wire size for a 550 amp service is, an 800 MCM copper conductor with an insulation factor of 90 degrees C. This conductor is rated at 555 amps. Parallel 250 MCM will give you a total capacity of 580 amps. A triple run of 2/0 will give you a total capacity of 585 amps.
600amps
This is a voltage drop question. To answer this question a voltage has to be stated. The higher the voltage to the circuit becomes the smaller the wire size needed. After a certain voltage point the wire size will remain constant and the voltage drop at the load will become smaller.
You obvioulsy do not know what you are talking about. The question as stated makes no sence.