#8 is the size of wire to use for grounding a 100 Amp panel. Green is color used for grounding #8 is code.
In a 200 amp service panel, the ground wire is typically a bare copper wire or green insulated wire. It is connected to the ground bar within the panel. Make sure to consult the manufacturer's instructions or a licensed electrician for guidance specific to your installation.
In the service distribution panel there are termination points at the top of the panel. Two of the utilities "hot" conductors terminate on the main breaker. The neutral utility termination point is on a terminal block usually off to the side near the main hot terminations. It is in this neutral termination block where the system ground connects from the ground rods to the distribution panel. For a 100 amp panel the wire size will be a #6 bare copper conductor.
For a 200 amp service, you would typically use a 4/0 AWG copper wire for the grounding wire running between the meter box and the service panel. This size is suitable for carrying the necessary current and providing proper grounding protection for the electrical system.
The size of the ground wire for a circuit is typically based on the size of the circuit breaker protecting that circuit. For a 200 amp circuit breaker, the recommended ground wire size is 4/0 AWG (American Wire Gauge) copper wire. This wire size helps ensure that the ground wire can safely carry any fault currents that may occur in the electrical system.
You can install a 100 amp sub panel off a 60 amp main panel fed by 100 amp service. This allows for the sub panel to be adequately powered with headroom for future circuits or expansions. It is important to ensure the wire size from the main panel to the sub panel is sufficient to handle the load.
#6 bare copper wire.
200 amp service in chicago uses 3 aught.
In a 200 amp service panel, the ground wire is typically a bare copper wire or green insulated wire. It is connected to the ground bar within the panel. Make sure to consult the manufacturer's instructions or a licensed electrician for guidance specific to your installation.
In the service distribution panel there are termination points at the top of the panel. Two of the utilities "hot" conductors terminate on the main breaker. The neutral utility termination point is on a terminal block usually off to the side near the main hot terminations. It is in this neutral termination block where the system ground connects from the ground rods to the distribution panel. For a 100 amp panel the wire size will be a #6 bare copper conductor.
Almost any average size home today will requre a 200 amp service panel.
AWG 2/0 copper.
In Canada it is a #6 bare copper conductor that connects the grounding rod or plate to the neutral point in the distribution panel.
A 200 amp service panel with a 60 amp sub-panel.
The recommended ground wire size for a 100 amp sub panel installation is typically 8 copper wire.
Answer for USA, Canada and countries running a 60 Hertz supply service.CEC states that a #3 bare copper conductor is a common grounding conductor size for a 200 amp service panel and it is the minium size for service raceway and service equipment of 400 amps.
For a 200 amp service, you would typically use a 4/0 AWG copper wire for the grounding wire running between the meter box and the service panel. This size is suitable for carrying the necessary current and providing proper grounding protection for the electrical system.
Use #10 copper.