Use a 15 amp breaker and 14 AWG wire and all switches and outlets rated at 15 amps or greater.
For a 15 amp circuit, it is recommended to use 14-gauge wire.
For a 15 amp circuit, a 14-gauge wire should be used.
For a 15 amp circuit, a 14-gauge wire should be used.
14 AWG.
Not unless you change the wiring for that circuit. The breaker protects the wiring and if you install a 40 amp breaker on a 15 amp wire circuit you will have a fire in your home.
12 amps is 80% of a 15 amp circuit which is the maximum that should be run. Other factors such as wire size and length also play a part in calculating a safe maximum Jeff
A circuit breaker protects the wires that the devices are connected to. If the devices that are connected to the circuit are 20 amps the wire size should be #12 wire fed from a 20 amp breaker. This breaker should not trip unless the circuit is overloaded or a fault occurs on the circuit. If the devices that are connected to the circuit are15 amps the wire size should be #14 wire fed from a15 amp breaker. This breaker should not trip unless the circuit is overloaded or a fault occurs on the circuit. Putting 20 amp sockets on this 15 amp circuit will work but the circuit is limited to the amount of load that can be plugged in. You will not get the full capacity of the 20 socket because the breaker will trip at 15 amps.
A 14 gauge wire is typically used on a 15 amp circuit breaker. It is not recommended to use a larger circuit breaker with a smaller wire size as this can create a fire hazard.
The appropriate wire size for a 20 amp circuit is typically 12-gauge wire.
For a 25 amp circuit, the appropriate wire size is typically 10 gauge wire.
The appropriate wire size for a 30 amp circuit is typically 10 gauge wire.
The appropriate wire size for a 50 amp circuit is typically 6-gauge wire.