answersLogoWhite

0


Best Answer

You might think this is a good idea, but it isn't. The code requires a single cable of the required current carrying capacity. What would happen if one of the cables was damaged and the hot wire severed. Then the other would be carrying 40 amps and you wouldn't know it until your house burned to the ground.

<<>>

No, the electrical code states that no conductors of similar conductivity in sizes smaller that #1/0 copper shall be permitted in parallel.

User Avatar

Wiki User

12y ago
This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: Can you use 2 runs of 12 gauge wire in for 40 amps circuit?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

14 gauge wire can be on what size circuit breaker?

A 14 gauge wire is typically used on a 15 amp circuit breaker. It is not recommended to use a larger circuit breaker with a smaller wire size as this can create a fire hazard.


What size of wire needed for 220volt?

The size of wire needed for a 220v circuit depends on the amperage of the circuit. For a typical 220v circuit at residential settings, a 10-gauge wire size is commonly used for 30 amps, while larger circuits may require 8 or 6-gauge wire for higher amperage ratings. It is important to consult with a licensed electrician to ensure the correct wire size is used for your specific application.


What type of wire gauge should be used for a 20-amperes circuit?

For a 20-amperes circuit, a wire gauge of at least 12 AWG should be used to ensure safe and efficient operation. Choosing the correct wire gauge will help prevent overheating and potential hazards in the circuit.


How many amps will 4 gauge wire handle?

The amps that a four gauge wire will handle will depend with the thickness of the wire. If the wire is thin, the four gauge will handle 95 amps.


What gauge cable to run 240 volts?

For a 240-volt circuit, you should use a cable with a gauge appropriate for the amperage of the circuit. Commonly used sizes include 10-gauge wire for up to 30 amps, 8-gauge wire for up to 40 amps, and 6-gauge wire for up to 55 amps. Ensure to consult local building codes and a qualified electrician for specific requirements.


Can work wire for 100 amps use for 60 amps circuit?

Using a wire rated for 100 amps for a 60-amp circuit is generally fine. It's important to ensure that the wire gauge matches the amperage requirements to prevent overheating and potential fire hazards. Check local electrical codes to confirm that it is within regulations.


Does a 20 amp circuit require a number 12 gauge wire?

Yes, a 20 amp circuit typically requires a minimum of a number 12 gauge wire to handle the current safely. Using a smaller gauge wire could lead to overheating and potentially a fire hazard. Always follow the electrical code requirements for wiring circuits.


What gauge wire is needed for 60 amp circuit?

A #6 copper wire with an insulation factor of 75 and 90 degrees C is rated at 65 amps.


Is it safe to parallel 10 gauge wire for 60 amps?

No, it is not safe to parallel 10 gauge wire for a 60-amp circuit. You should use a wire size that is rated for the amperage of the circuit to ensure it can handle the load safely and prevent overheating. In this case, you should use a minimum of 6 gauge wire for a 60-amp circuit.


What wire gauge is needed for a single phase 60 amp circuit?

#6 wire is good for 65 Amps as long as it is type THHN.


How many amps will 4.0 gauge wire carry?

140 AMPS


What is the amp rating for a 3 wire?

A 3-wire circuit could have different amp ratings depending on the type of wire and the application. In residential settings, a common amp rating for a 3-wire circuit is 20 amps, which is typical for general-purpose lighting and outlet circuits. It's important to consult the local electrical code or a professional electrician to determine the appropriate amp rating for a specific 3-wire circuit.