answersLogoWhite

0


Best Answer

That depends on what temperature-rise you'll accept, and on what type of coating

or jacketing surrounds the cable, and on the airflow around the cable.

User Avatar

Wiki User

12y ago
This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: How many amps taken 1 sq-mm copper cable?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

How many amps will taken in sq mm copper wire?

10 amps


How many amps for a 0.75mm cable?

5 amps


How many amps is 6mm cable rated at?

6mm2 cable is rated at 40amps


How many amps can a 2.5 sq mm wire conduct?

It will taken 8 amps <<>> The conversion of 2.5 sq mm wire to AWG is equal to a #12 wire. The ampacity of a #12 copper wire with an insulation factor of 90 degrees C is 20 amps.


How many legal amps can a 35mm cable conduct?

44.8AMPS


How many amps will taken by 1sq mm alluminium wire?

1 mm2 aluminium wire is not easy to buy but 1 mm2 copper wire is rated at 10 amps. Since the conductivity of aluminium is 7/12 that of copper, 1 mm2 aluminium wire would be rated at 7½ amps max (the same amount of heat is produced per metre by a current of sqrt(7/12) times that for copper).


How many amps can a 125 mm2 section cable carry?

The current carrying capacity of a cable can depend on factors such as the material, insulation, and installation method. For a rough estimate, a 125 mm2 cable can typically carry around 200-250 amps for standard copper conductors in common installation conditions. It is advisable to consult local electrical codes and standards, as well as a qualified electrician, for precise calculations.


How many Amps is number 4 THHN copper rated for?

According to the National Electrical Code (NEC), the ampacity of a 4 AWG THHN copper wire at 75°C is 85 amps, and 95 amps at 90°C.


How many volteged do you lose in 50 feet out of copper?

That depends on how much current (Amps) is flowing through the copper. The voltage you lose in the copper will always be (A) times (R). 'A' is the current (amps) in the copper. 'R' is the resistance of the copper. You can look that up in a product catalog, or measure it with a really good ohm-meter.


How many amps capacity will a number 00 copper conductor allow?

A 2/0 copper conductor with an insulation rating of75 and 90 degrees Care rated at 175 and 185 amps respectively.


How many amps will a 2 0 wire carry?

If you mean 2/0 copper wire it is rated 175 amps. # 2 wire is 115 amps. If you are referring to 2.0 metric it is rated 15 amps.


How many amps service does 12 gauge yellow wire hold?

The normal current capacity of 12 AWG copper wire is 20 amps.