It's necessary to look at the dyer to see how much current it uses, which should be on the maker's plate near where the cable enters the appliance. If it uses less than 50 amps, a 50 amp cable is all right.
You can use #6 that is rated for 55 amps but not the receptacle that is rated for 50 amps. The 30 amp configuration of a dryer plug will not fit in the configuration of a 50 amp receptacle. The breaker feeding the # 6 wire will have to be still a 30 amp breaker because the rating of the dryer cord is still only 30 amps. Remember the breaker protects the wire size.
The correct configuration for a dryer circuit is; 30 amp breaker feeding a three wire #10 cable that connects to a four wire dryer receptacle, NEMA # 14-30R. This receptacle is a 125/230 volt, three pole four wire grounding outlet. From the cable to terminal connections on the receptacle; black to X, red to Y, white to W and bare ground to terminal G. Remember to wrap fasten the ground wire to the junction box's ground terminal screw before termination it on to the receptacle's ground terminal
Yes you can as long as it is feed off of a 20 amp circuit in at least #12 gauge wire.
Yes you can because it is rated for 30 Amps. You need to be sure you have a good connection to the receptacle because it isn't designed for the larger wire in most cases.
Maybe not. Since there is no wire with a rating of 50 amps exactly there may be 60 amp wire already installed. Range's use a #8 wire with 50 amp range receptacle for its circuit. If the wire that is installed now is # 6, that is good for 65 amps, then no wire needs to be changed. The only 60 amp receptacle that will be allowed on the 60 amp cable is a three pole four wire grounding 125/250 volt device. The number will be 14-60R. There is a three phase rated receptacle in the three pole four wire grounding type. It is a 15-60R.
You can use the wire rated for 20 amps on a 15 amp receptacle but you can not use a 20 amp fuse on any device rated at 15 amps. This is a tricky part of the code about receptacle outlets, You can use a 15 amp duplex outlet on a 20 amp circuit. (duplex outlet two devices can plug in) If it is a single outlet then the outlet must be rated 20 amp. NEC table210.21(B)(3). ============ A 15 amp duplex receptacle can be wired to a 20 amp rated circuit. This means the breaker OR fuse protecting the circuit can be rated 20 amps if the wire is also rated at 20 amps (12 AWG). --Sparkfighter
In countries that use a single phase split secondary service you can. In modern homes this is the type of circuitry that is used for kitchen split receptacles. On the receptacle the tie bar is removed from the "hot" side of the receptacle. A red wire of the three wire cable is placed on the upper terminal of the receptacle. A black wire of the three wire cable is placed on the lower terminal of the receptacle. The white wire is placed on the opposite side of the receptacle under the silver coloured screw. This will give you a full 15 amps capacity on the top portion of the receptacle and a full 15 amp capacity on the bottom half of the receptacle.
You can do a 30 amp twist lock receptacle 220v 3 wire (nema L6-30R) or a strait blade 30 amp 220v 3 wire receptacle (nema 6-30R) or a traditional 30 amp dryer plug. The nema # is a universal # that everyone uses to identify that plug. Ask for it. The most important part is the 30 amp male that your trying to plug in. Match it up with what you putting in the wall. Use #10 gauge wire for 30 amps
No. You need 20 amp receptacles. ( if a single receptacle on an individual brach circuit NEC 210.21 (B)(1) ) Yes you can use a 15 amp receptacles on a 20 amp breaker in the states but not in canada. ( branch circuit supplying two or more receptacle NEC 210.21(B)(3) ) 15 amp receptacle on a 20 amp circuit is not code, partly because 20 amp circuits use #10 ga wire, which does not fit unto a 15 amp receptacle,(can be forced but lots of work.) Also a 15 amp receptacle will not take the 18 amps continuios that a 20 amp recep. will. ( It is code, see above. 14 awg = 15 amp, 12 awg = 20 amp, 10 awg = 30 amp ) 20 amp wire is 12 gauge not 10 Yes you can use 15A outlets and swithes on 20 amp breakers they are UL listed for 20 amp even if they are stamped for 15A as long as the wire is 12ga to. ( NEC Table 210.21 (B)(3) )
No there are no adapters made for these types of installations. The reason there are no adapters is to provide a factor of safety. To plug a 30 amp plug into a 50 amp receptacle could allow 50 amps to be applied to a 30 amp rated cord. The 50 amp receptacle is more than likely being fed by a 40 amp breaker. Just change the plug cord to match the ampacity of the breaker ahead of the 50 amp receptacle. Or change the 50 amp receptacle and 40 amp breaker to a 30 amp breaker and use your existing cord plug.
Use the 4 wire if possible. You would only use a 3 wire for an old appliance.You shouldn't if possible. The 3 wire has no neutral wire as the 4 wire does. Som applications require the use of a 3 wire and some don't.
A breaker box circuit fuse? Check the wire size. 14gauge use 15amp. 12 gauge use 20 amp.
You can if you have the existing materials. If you want to keep your costs down the same installation can be installed with the following materials. For wire all that is needed is 3C #8 wire. For the breaker a two pole 40 amp will work. You will need a 4 11/16" square box to install the range receptacle into.
If you have 100 amp wire, you can use it for a 60 amp circuit, or for any circuit of 100 amps or less. But if you have a 60 amp circuit, 60 amp wire is thinner and cheaper than 100 amp wire.