answersLogoWhite

0

10 AWG in copper.

User Avatar

Wiki User

13y ago

What else can I help you with?

Related Questions

What size ground wire needed for 75 amps at 208 volts?

#8 copper


What size generator is needed to run a refrigerator?

Depending on size of Fridge. But AVERAGE is 12 volts for fridge, circuit necessity 15 amps 15 amps X 120 Volts=1800 watts minimum...I'm LEARNING myself


What minimum fuse rating is needed for a 12 volt circuit when using one 48 watt bulb?

The formula you are looking for is Watts = Amps x Volts. Amps = Watts/Volts. This comes to 4 amps load. Minimum size fuse would be 5 amps.


What size wire to carry 8 amps at 120 volts?

A # 14 copper conductor will be fine to carry 8 amps at 120 volts. This size conductor is rated at 15 amps.


What wire size needed for a RV 30 amp 120v at 90 feet?

For single phase 30 amps at 120 volts you would need a #8 copper wire with an insulation rating of 90 degrees C.


What size wire do you need to carry nineteen amps for two hundred feet at two hundred forty volts ac?

10 guage


How do you solve for the size of wire when the given is kva?

The V stands for volts and A is amps. If for example you have a 12kVA device and are running off a voltage of 120 volts then Amps = 12000/120 = 100. You then use the calculated amps in a wire size table to get the correct size.


What size breakers are needed for two 500 watt baseboards?

Each baseboard heater will draw a little over 4 amps at 120 volts or 2 Amps at 240 volts. The total number of baseboards on a circuit will draw the sum of these amps. Keep the load under 80% of the amperage rating of the breaker.


What effect are there when resistance is increased in the size of the current?

Current is inversely proportional to resistance. If you double the resistance, you halve the current. Ohm's Law: Volts = Amps * Ohms Solve for Amps: Amps = Volts / Ohms


Are fuses sized on amps and volts?

Fuses are rated in Amps. Although the physical size of a fuse is to do with volts; the further the terminals are apart the less likelihood there is of 'sparkover' between them.


What is the wire size for 50 feet distance 120 volts 12 amps?

For a 50 feet distance with 120 volts and 12 amps, you should use a 14-gauge wire to ensure electrical safety and efficiency. A 14-gauge wire is rated to handle up to 15 amps for household wiring applications.


What size wire do you need for 650 watts?

To answer this question a voltage needs to be stated. Wire is sized by the amount of amperage the load takes. W = Amps x Volts. Amps = 650/ volts.