The name plate, which is a metal plate on the back of the appliance with a lot of technical information on it, may tell you straight up what size the circuit needs to be. If it doesn't it will most certainly give you the wattage of the freezer. For single phase systems such as in a home, take that number, divide by the voltage, which gives you amps, and choose the next size larger breaker and corresponding wire size.
Normally AWG #10 wire on a 30 amp breaker but it really depends on the size of the pump. The pump manufacture will specify the size wire and size breaker needed.
A minimum of 15-amp breaker is "needed", but a 20-amp is often required by electrical code for that situation.
The size of the breaker needed for a 220V wall heater depends on the current rating of the heater. Generally, for a 220V heater, a 20-amp breaker is common. However, it's important to check the manufacturer's specifications and local electrical codes for the appropriate breaker size.
To determine the size of the breaker needed for a 78 amp range, you typically need to use a breaker that is the next size up from the amp rating. This means that you would need an 80 amp breaker to safely accommodate the 78 amp range. However, always consult with a qualified electrician to ensure the correct breaker size for your specific electrical setup.
A 220V hot water heater typically requires a double-pole breaker rated at 20-30 amps, depending on the specific power requirements of the water heater. Make sure to consult the manufacturer's specifications or a qualified electrician to determine the appropriate breaker size for your specific unit.
The 225 amps is the secondary output amperage. Look on the machines nameplate to find the input amperage. It is that amperage that is needed to size the feed wire and there the breaker size. When you find that amperage you may want to re question the breaker size.
In standard construction this would require a 15 amp breaker and 14 gauge copper wire.
A 5500 watt gas powered generator typically requires a 30 amp breaker for a 240 volt connection. It is recommended to consult the manufacturer's specifications to ensure the correct breaker size for your specific generator model.
50 ft freezer how size compressor
Wire size is calculated from the amount of current the load draws. More information is needed. Voltage and amperage will do fine.
one the size of your mom
20 amp In North America code states a two pole 15 amp breaker will do the job.